Man, this is a pain in the ass. Before wiring in another panel I decided to try and add a 10ga neutral onto my 8ga. Ghetto yes..but I wanted to see if it would make any difference.
I took off the surge protectors and fired everything back up. Two of the breakers tripped in about 10min.
The symptom seems to be induction heating of the breakers...Nothing else gets hot. ALL of the wires are cold. Once I flip off the power the neutral bar is barely warm. The bus bars actually aren't that hot either.
My current plan is to just add another panel and have them wired so they *could* run 4 lights each. This panel seems to be happy enough with 4 lights.
what a PITA. Any other ideas for a quick fix?
Hmm...
Do you have access to a true RMS clamp-on ammeter? I'm thinking it would give you insight into the exact nature of your load on each of the conductors.