WOW! What a thread, yet I am still a bit confused as to how to calculate my situation, which will be:

Running 8 1000w lights, under Adjust-A-Wing Reflectors (not air cooled), ballasts outside the 20' x 25' room, 2 8" Max Fans for intake and 1 14" Max Fan for exhaust (filtered by a Phresh Filter), as well as a total of six wall mounted fans and six stand fans (all 18"). No CO2 (that is, natural CO2 will come in through the two 8" intakes), and lights will be running at night 7:00pm-7:00am, at a CA elevation of about 3200 ft. Winter nights get down to 40-50 degrees outside, and I am not sure what Summers outside temps will be at night (maybe 60-70 degrees).

I want the AC unit to serve as a dehumidifier while the girls sleep and cool the room when lights are on. The intake and exhaust fans will likely run continually while the girls take in light...

I'm considering the Ideal Air Mini Split units...

How many BTUs do I need for the AC unit?
Maripan is offline Quote


Old 04-14-2013, 12:35 AM #122
RomulusUSA
Member

Join Date: Jan 2011
Posts: 420
RomulusUSA will become famous soon enoughRomulusUSA will become famous soon enough
I have a question folks! Hopefully I can get some pro input.

Last summer, I ran 1000w 12/12 and 500w 24/0. I cooled it with a 5.6k window ac unit that was boxed up. According to the table provided in the first post of this thread, I needed 18.9kBTU last year to maintain temps, but I was able to hold low 80s with 5.6k. I assume this is somewhat due to my climate, etc. Or the table just over calculates, which I know is what about 50% of HVAC contractors do lol.

This summer, I will be running 2kW 12/12 and 1.5kW 18/6. The calculator says I need 28.5kBTU to maintain temps. I am having no luck finding a used 18-24kBTU unit at this time, and don't really want to spend $600ish on a new 24k unit. How do you guys suspect a 12k would do. I am worried it will be undersized and I'll run into issues... Input plz!
__________________
"Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety." - Benjamin Franklin

Spring 2013 20 gallon AirPot grow
RomulusUSA is offline Quote


Old 05-23-2013, 11:10 PM #123
Jnugg
Senior Member

Jnugg's Avatar

Join Date: Feb 2006
Location: S.E. USA
Posts: 1,720
Jnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the rough
According to the main post,I need an 8000 to 10000 BTU a/c.

Room Dimensions = Roughly 12' x 12' x 8' high ceiling (This does not include the 2' x 8' closet).

Lighting = Bare bulb vertical 400w HPS

Fans and equipment = 1x 4" 170cfm inline centl exhaust fan,1x 12" fan on ground pointed up at bulb.170cfm fan is rated 65w,and the floor fan is rated 45w.

Room occupants = 1

So I did the calculations/math and this is what I came up with...

Room BTU's for 12' x 12' room = 5760 BTU's

Equipment BTU's = 385 BTU's

Lighting BTU's = 1600 BTU's

Room Occupant BTU's = 400 BTU's

Total BTU load = 8145 BTU's

If I include the closet in the room that makes the room roughly 12' x 14' and bumps Room BTU's up from 5760 BTU's to 6720 BTU's bumping the total BTU load from 8145 BTU's to 9105 BTU's.

Here's the thing.I'm growing in a 3' x 3' x 6' SJ DR90II placed in the 12x12 / 12x14 room,so basically using the room as a lung room so to speak,for the tent to draw it's fresh/cool intake from,and exhausting into the attic.

Does that seem about right for what I'm doing?

I'm wanting to bring the temp of the room down to 65°F/68°F as I already know my exhaust fan with bulb on in tent brings the tent to about 10° F aFbove ambient,so that I can keep tent temps during lights on at 75°F-78°F, and lights off temps 65°F/68°F.

So should I shoot for a 8000/9000 BTU unit or a 10000 BTU unit,or since I'm growing in a tent in the room,and the tent having active exhaust/passive intake should I be looking at something slightly smaller?
Jnugg is offline Quote


Old 05-24-2013, 02:20 AM #124
Jnugg
Senior Member

Jnugg's Avatar

Join Date: Feb 2006
Location: S.E. USA
Posts: 1,720
Jnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the rough
Quote:
Originally Posted by Jnugg View Post
According to the main post,I need an 8000 to 10000 BTU a/c.

Room Dimensions = Roughly 12' x 12' x 8' high ceiling (This does not include the 2' x 8' closet).

Lighting = Bare bulb vertical 400w HPS

Fans and equipment = 1x 4" 170cfm inline centl exhaust fan,1x 12" fan on ground pointed up at bulb.170cfm fan is rated 65w,and the floor fan is rated 45w.

Room occupants = 1

So I did the calculations/math and this is what I came up with...

Room BTU's for 12' x 12' room = 5760 BTU's

Equipment BTU's = 385 BTU's

Lighting BTU's = 1600 BTU's

Room Occupant BTU's = 400 BTU's

Total BTU load = 8145 BTU's

If I include the closet in the room that makes the room roughly 12' x 14' and bumps Room BTU's up from 5760 BTU's to 6720 BTU's bumping the total BTU load from 8145 BTU's to 9105 BTU's.

Here's the thing.I'm growing in a 3' x 3' x 6' SJ DR90II placed in the 12x12 / 12x14 room,so basically using the room as a lung room so to speak,for the tent to draw it's fresh/cool intake from,and exhausting into the attic.

Does that seem about right for what I'm doing?

I'm wanting to bring the temp of the room down to 65°F/68°F as I already know my exhaust fan with bulb on in tent brings the tent to about 10° F aFbove ambient,so that I can keep tent temps during lights on at 75°F-78°F, and lights off temps 65°F/68°F.

So should I shoot for a 8000/9000 BTU unit or a 10000 BTU unit,or since I'm growing in a tent in the room,and the tent having active exhaust/passive intake should I be looking at something slightly smaller?

Anyone?
Jnugg is offline Quote


Old 05-24-2013, 03:54 AM #125
Rolldaddy
Member

Rolldaddy's Avatar

Join Date: Feb 2012
Posts: 738
Rolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura about
Jnug

A 10000 btu ac should be fine for you. Maybe a bit larger could be better incase you ever want to add more light. If an ac is oversized it just means the compressor will cycle on less often
Rolldaddy is offline Quote


Old 05-24-2013, 04:05 AM #126
Jnugg
Senior Member

Jnugg's Avatar

Join Date: Feb 2006
Location: S.E. USA
Posts: 1,720
Jnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the rough
I would like to use more light....someday but no time too soon (maybe the next rental).

Too my understanding,if one has too large a unit that it will cool the room fine,but may just as well not dehumidify the room properly.
Jnugg is offline Quote


Old 05-24-2013, 04:28 AM #127
Rolldaddy
Member

Rolldaddy's Avatar

Join Date: Feb 2012
Posts: 738
Rolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura about
The more time your compressor is running the more your ac will dehumidify. Bigger is better, specially if you plan to use more light in the future but its up to you

If you want your ac to dehumidify more buy an undersized ac
Rolldaddy is offline Quote


Old 05-24-2013, 04:44 AM #128
Jnugg
Senior Member

Jnugg's Avatar

Join Date: Feb 2006
Location: S.E. USA
Posts: 1,720
Jnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the roughJnugg is a jewel in the rough
Right and I live in Fla which is hot damn near 10 months out of the year,and humidity jesus it is swampland afterall.So if I get too big a unit,I'll be cooling just fine,but humidity could stay high making it feel clamy/balmy in the room.I'd hate to have to buy and run a dehumidifier as well because I only have a 20 amp circuit to use (it controlls the entire rear of apt) and to stay within the 80% safe load I can't use more than 1840w and light,fans,with 10000 BTU unit will put me damn close.
Jnugg is offline Quote


Old 07-22-2013, 02:42 PM #129
Jhhnn
Senior Member

Join Date: Jan 2013
Location: Denver CO
Posts: 4,949
Jhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant future
Quote:
Originally Posted by Jnugg View Post
Right and I live in Fla which is hot damn near 10 months out of the year,and humidity jesus it is swampland afterall.So if I get too big a unit,I'll be cooling just fine,but humidity could stay high making it feel clamy/balmy in the room.I'd hate to have to buy and run a dehumidifier as well because I only have a 20 amp circuit to use (it controlls the entire rear of apt) and to stay within the 80% safe load I can't use more than 1840w and light,fans,with 10000 BTU unit will put me damn close.
I think that in some situations, growers would do well to have 2 units. One that's definitely too small, set to a temp it can't maintain. It'll run all the time, both cooling & dehumidifying. Then a second unit set to a higher temp to pick up the load when the light is on, which will both cool & dehumidify as it cycles on & off.

Some of the newer window units use the inverter tech to achieve much the same effect.

Here in Denver, high humidity isn't a big problem. If anything, the opposite is true. Winter humidity is often quite low, and when the air is heated to the human comfort range, it'll plunge to nearly nothing. W/O a humidifier, the plants need large amounts of water.
Jhhnn is offline Quote


Old 11-14-2013, 07:08 PM #130
2nd_nature
Newbie

Join Date: Oct 2013
Posts: 17
2nd_nature is on a distinguished road
Super informative. Awesome.
2nd_nature is offline Quote


Post Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT +2. The time now is 10:22 AM.


Click to Visit Sweet Seeds


This site is for educational and entertainment purposes only.
You must be of legal age to view ICmag and participate here.
All postings are the responsibility of their authors.
Powered by: vBulletin Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.