Old 06-24-2012, 06:00 PM #111
3TL
New Member

3TL's Avatar

Join Date: Jul 2011
Posts: 8
3TL is on a distinguished road
Hello everyone.

i have a wooden house built outside, corrugated iron roof. Its is 8m x 3m x 2.4m.
Inside will be 16 x 400w (6.4kw) HPS.

I have calculated that i need about 36 000 btu's to keep it pleasant. In summer highest temps are about 104 fahrenheit. Can run the lights at night for more cooling power.

Question i have are:

1.When running an aircon can you somehow attach a carbon filter? If not what about smell?
2.Are you supposed to have just the aircon or must you have and intake and exhaust fan as well? What cfm should they be? i assume if the fans are too powerful they will end up throwing cool air out then the air con must work harder?
3.If you use an aircon with too many btu's will it cycle on and off causing humidity problems?
4.I plan on putting some kind of insulation on the walls and roof, what is best?

Thanks for any of your help. I really appreciate it.
3TL is offline Quote


Old 07-15-2012, 04:46 AM #112
Nor'Easter
Member

Join Date: Oct 2009
Posts: 889
Nor'Easter is just really niceNor'Easter is just really niceNor'Easter is just really niceNor'Easter is just really niceNor'Easter is just really niceNor'Easter is just really niceNor'Easter is just really niceNor'Easter is just really niceNor'Easter is just really nice
So bottom line how much AC do you need in the Northeast in the summer in a basement for a 7 by 7 with 2 lights?
Edit: I since started my own thread on the subject so please check it out. peace
__________________
"Those who would sacrifice liberty for security deserve neither." -Ben Franklin.

In Greed We Trust- that is the true highway to hell
Nor'Easter is offline Quote


Old 07-26-2012, 06:56 PM #113
chase
Guest

Posts: n/a
?? Quote:
Originally Posted by chase
Hello everyone ,im going to try a new set up .
please tell me if this will work.

1000 Watt H.P.S 10000 btu portable ac , & I intend to air cool the light with an 8 inch vortex pulling from the room , & blowing into the same room , through a carbon filter , recycling the hot air.


Will the ten thousand btu ac keep everything cool ? Any info would be apreaciated.
\
Also I cant duct out , only a small laundry duct for my ac.




This will be a 4x4 room , & the lights will be 12/12. Also the electronic balist will be in the same room but outside of the polysheild that I will be flowering in , I will have an oscelating fan also.
Quote


Old 07-26-2012, 06:59 PM #114
chase
Guest

Posts: n/a
^^^^ this seamed like it might be a better place to post this , If my ? is unclear , then please be patien , & I will try to help you with my wording.
Quote


Old 07-26-2012, 07:15 PM #115
chase
Guest

Posts: n/a
Also im in Del norte by the ocean right by the oregon border it never gets hot just wet.
Quote


Old 07-26-2012, 10:37 PM #116
Rolldaddy
Member

Rolldaddy's Avatar

Join Date: Feb 2012
Posts: 738
Rolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura about
Chase,

If you are recirculating the hot air from your light and not dumping out the hot air then your not utilizing your air cooled light.

If you have a carbon scrubber and an air cooled light you might want run them separately. One duct bringing air into and dumped out of your hood directly so that it doesn't mix with the air in your room. Then you exhaust or recirculate the air from the scrubber.

I hope that helps and you get what I'm saying. If not you can ask to clarify here or by PM. Either is fine
Rolldaddy is offline Quote


1 members found this post helpful.
Old 07-26-2012, 10:44 PM #117
chase
Guest

Posts: n/a
Thank you for the reply

Ok so then with no way for me to duct out the hot air , should I scrap the air cooled light idea , & just cool with the 10000 btu portable .There is a laundry duct that I can safely duct my ac out of , but too many close neibors to duct hot air out of the window safely.
Quote


Old 07-27-2012, 08:41 PM #118
Rolldaddy
Member

Rolldaddy's Avatar

Join Date: Feb 2012
Posts: 738
Rolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura aboutRolldaddy has a spectacular aura about
Your welcome. If you find my post helpful I'd appreciate it if you click the yes link on the bottom of my post.

As for the air cooled light you can you can dump out the hot air through the dryer vent with the ac exhaust. You can also just dump that hot air into your attic also. If you hook the fan to the air cooled light properly the exaust should not smell. Or you do what you said and scrap the idea of air cooling your hood. If a light isn't cooled it creates about 5000 btu of heat. If it is cooled 3000 btu is a good number to use to calculate how much of a load it will pit on your ac. So if your portable ac really cools 10000 btu's your light will use half and depending the size of your room and how hot it is the other 5000 btu might be enough for the room


The exhaust I would be more concerned with if I was you would be the ac exhaust because that exhaust is likely to carry out air from inside your room. IE the ac exhaust will smell like your room

I believe you said you have an air scrubber. If so you will want to design a recirculating
system to keep the smell down in the room as much as possible

Good luck
Rolldaddy is offline Quote


1 members found this post helpful.
Old 08-08-2012, 03:19 AM #119
smithsutton
Member

smithsutton's Avatar

Join Date: May 2009
Location: planet earth for now
Posts: 103
smithsutton will become famous soon enough
Quote:
Originally Posted by G33k Speak View Post
I go with 5000 BTU's per 1W of light.
i go with these numbers also and it does verry well over the last 10 years ..

thanks for the other mind numbing numbers .. and yes i do understand them .. also digital term controls are also more accurate than analog controls on the the a/c unit .. also if u use a room a/c set it on a table that sets about middle hight of the room i way increases the efficiency of the cooling because heat rises ..

peez ..

ss ..
__________________
cant never did anything .. visit hippe hill college grove tn .. was an overgrow member since 2000 ..

ahh the bangger (~shabang~) hes gone but not forgotten .. peace where ever u are brother ..
smithsutton is offline Quote


1 members found this post helpful.
Old 11-09-2012, 08:59 PM #120
Mr frost
Guest

Posts: n/a
Quote:
Originally Posted by chase View Post
Also im in Del norte by the ocean right by the oregon border it never gets hot just wet.
i had a of a clone of del norte chem dog it was a cut that is fuckn dank have you seen this around del norte i hade it a while back i got it in northern humboldt county i wish i would have hung onto that cut
Quote


Post Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT +2. The time now is 10:24 AM.


Click to visit Twilight Labs


This site is for educational and entertainment purposes only.
You must be of legal age to view ICmag and participate here.
All postings are the responsibility of their authors.
Powered by: vBulletin Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.