Powerbox has been banned in Canada, distributor was forced to no longer carry them.
|
|
|
1 members found this post helpful. |
|
|
#32 |
|
Member
Join Date: Apr 2014
Posts: 178
![]() |
Opened the door and the lights were off,checked my Titan controller,and it looked like it stopped 20 minutes after lunch lights came on.Went to check my electric panel,my 50 amp breaker popped so i knew something was up.I flipped it back ,lights came on then 15 minutes later breaker popped again.Ran to the room and there was a burnt smell and fumes coming from that controller.
Opened the controller and found that the red hot wire terminal was burnt.Very thankful there was no fire and also disappointed in this thing,it’s not even a year old. |
|
|
|
|
|
#33 | |
|
Senior Member
Join Date: Jun 2016
Posts: 2,094
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Quote:
|
|
|
|
|
|
|
#34 |
|
Going Deep
![]() Join Date: May 2016
Posts: 722
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Yes, On #19 in this thread, I'm mentioned that I brought the Titan back. Glad you're ok.
|
|
|
|
|
|
#35 |
|
Member
Join Date: Apr 2014
Posts: 178
![]() |
BTW this was a Titan Helios 7 which controls up to 8k lights with a built in timer.
|
|
|
|
|
|
#36 |
|
Member
Join Date: Apr 2014
Posts: 178
![]() |
Thanks Zeez,i am going to go to the store to get it exchanged,but have to wonder if this one was faulty or not?. I want to open it up completely but the sticker says “warranty void if opened”. I’ll ask the guy there if we can open it up just to see how far is the damage,cause i can tell that red lead on the inside was melted also.
|
|
|
|
|
|
#37 |
|
Member
Join Date: Jan 2013
Posts: 416
![]() ![]() ![]() ![]() ![]() |
What Guage of wire did you use, those ring terminals are only rated for 10AWG, 8AWG won't fit inside and allow you to crimp the wire.
|
|
|
|
|
|
#38 | |
|
Senior Member
Join Date: Jun 2016
Posts: 2,094
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Quote:
Is it possible the ground wire made contact with the hot wire? |
|
|
|
|
|
|
#39 |
|
Member
Join Date: Jan 2013
Posts: 416
![]() ![]() ![]() ![]() ![]() |
Possible, looks like none of the ring terminals are insulated, that's why they were taped. Do you have ratchet crimps?
|
|
|
|
|
|
#40 |
|
Member
Join Date: Jun 2014
Posts: 118
![]() ![]() ![]() ![]() ![]() ![]() |
It looks like he didn't have the wires screwed down tight to me. I have the same controller and it's worked nonstop for 3 or 4 years. I think think it said in the instructions to check your connections once a year. You are also supposed to use 6 awg wire for that controller. I'll be sure and check that my connections are tight after seeing that.