Gfci in subpanal?

Question about adding a gfci in my sub panel.

I have a 2 pole 40amp breaker feeding my sub, approximately 20ft away in my (attached) garage. The sub panel has 2 20 amp 2 pole breakers, one feeding a 18k mini split, the other 20 amp is feeding a lighting controller powering 10 lec315, (330 watts each). Everything was installed by a licensed electrician, following local codes.

For added safety I would like to add a gfci breaker. Should this be added to the 40amp main panel, or just a single 20 amp gfci 2pole in the sub panel for the lighting controller? I'm having the electrition over later this week and wanted some opinions from fellow growers. My buddy is a great electrition, he's just not that familiar with growroom SOP's.. thanks..
JJ Lowe is offline Quote


Old 05-30-2017, 07:06 PM #2
JJ Lowe
Member

Join Date: Sep 2014
Location: SoCal
Posts: 82
JJ Lowe will become famous soon enoughJJ Lowe will become famous soon enough
Anyone?
JJ Lowe is offline Quote


Old 07-27-2017, 01:29 PM #3
FlyinHawaiian
Member

FlyinHawaiian's Avatar

Join Date: Feb 2006
Location: Islands
Posts: 252
FlyinHawaiian is on a distinguished road
im not positive on this but i think some air conditioners wont run on GFCI circuits or maybe that was arc fault circuit breakers, i cant remeber lol so id ask ur elec guy.

id just run the one GFCI 20amp circuit breaker for your lights and keep the a/c circuit on a regular breaker
__________________
Maui MMJ patient
FlyinHawaiian is offline Quote


Old 07-27-2017, 02:10 PM #4
OldPhart
Member

OldPhart's Avatar

Join Date: Feb 2017
Posts: 339
OldPhart is a glorious beacon of lightOldPhart is a glorious beacon of lightOldPhart is a glorious beacon of lightOldPhart is a glorious beacon of lightOldPhart is a glorious beacon of lightOldPhart is a glorious beacon of lightOldPhart is a glorious beacon of lightOldPhart is a glorious beacon of lightOldPhart is a glorious beacon of lightOldPhart is a glorious beacon of lightOldPhart is a glorious beacon of light
If it is well installed (wires off floor and properly protected), there is no reasonable reason to have GFCI. I know I'm going to get flamed, but I have NEVER been shocked when things are well installed. I'm assuming you are bright enough to not stand in water and screw around with a running light. I have seen too many GFCIs cause issues. You do understand that a GFCI's only purpose is to protect against shock, it does NOTHING else?

PS, I wanted to add that the only thing I would suggest having on GFCI is the small/portable equipment which is often times run on a two prong plug. But these are the devices that are normally most critical such as fans/pumps. If it were me, I would not run GFCI on a grow, unless things are installed poorly or there are children in the grow. But that brings up a whole new set of issues.
__________________
My half assed seed run.
https://www.icmag.com/modules/Journa...journalid=1868

Last edited by OldPhart; 07-27-2017 at 02:27 PM.. Reason: ps
OldPhart is offline Quote


Old 09-03-2017, 11:44 AM #5
AvidLerner
Member

AvidLerner's Avatar

Join Date: Apr 2008
Location: Universe
Posts: 447
AvidLerner is just really niceAvidLerner is just really niceAvidLerner is just really niceAvidLerner is just really niceAvidLerner is just really niceAvidLerner is just really niceAvidLerner is just really niceAvidLerner is just really nice
you can install a GFCI breaker in your main panel. your sub panel already is loaded with 40a with 2-20a circuits. Adding a GFCI is easy you just replace a 20a circuit breaker already wired for outlets and replace with a same GFCI breaker and now you have additional protections. Whenever an outlet is within 5 feet of water GFCI is required by code.
__________________
I'm just a poor boy, I need no sympathy
Because I'm easy come, easy go
A little high, little low
Anyway the wind blows, doesn't really matter to me, to me.
AvidLerner is offline Quote


Post Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT +2. The time now is 03:24 PM.


Click for great deals at MB Ferts!


This site is for educational and entertainment purposes only.
You must be of legal age to view ICmag and participate here.
All postings are the responsibility of their authors.
Powered by: vBulletin Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.