grow room power

i want to design a 240v 30 amp circuit for a room i have because the house is wired with 15 amp 120/240v outlets.i want to know if i can put 2 1000w lights 8.4 amp total,T5 grow light .5 amp,2 inline fans 2 amps total and 2 ventilation fans 5 amps total on this new circuitt i want to build.so i have a total of 15.9 amps/16 amps on this circuit.is it safe to run all these appliances on the circuit without worries since it would be a 30 amp rated?

please and thank you
scratchgrow876 is offline Quote


Old 09-19-2015, 11:01 AM #2
Lazyman
Overkill is under-rated.

Lazyman's Avatar

Join Date: Jun 2009
Location: Norcal
Posts: 5,186
Lazyman is a splendid one to beholdLazyman is a splendid one to beholdLazyman is a splendid one to beholdLazyman is a splendid one to beholdLazyman is a splendid one to beholdLazyman is a splendid one to beholdLazyman is a splendid one to beholdLazyman is a splendid one to beholdLazyman is a splendid one to beholdLazyman is a splendid one to beholdLazyman is a splendid one to behold
Yes, as long as you keep the amp draw at or under 80% of the circuits rating for continuous duty use. The trick will be getting both 240v and 120v output from a 240v source. If you're good with wiring you can do it, if you don't know how I won't tell you.
__________________
*I'm fairly busy so please excuse my absence or slow responses to PM's!

All about Growroom cooling: Keepin' it cool man (my 1st published article)
How to automate reservoir top offs or most anything water-related
The only UV-B lighting thread worth a damn
CO2 for dummies

Big grow:
The 36KW medical/perpetual basement

Lazyman is offline Quote


Old 09-19-2015, 12:30 PM #3
Pinetar
Newbie

Pinetar's Avatar

Join Date: Sep 2015
Posts: 41
Pinetar will become famous soon enough
You will be safe with 16 amps on a 30 amp circut. In growroom design area the sticky for "growroom electrical and wiring" has some good tip and pics to explain. If you don't understand please get professional help, peace of mind on electrical installations is priceless
Pinetar is offline Quote


Old 12-01-2015, 03:14 AM #4
jimbo9414
Newbie

Join Date: Nov 2015
Posts: 5
jimbo9414 is on a distinguished road
hi...retired electrician here....I would run a 10-3 (2 hots, neutral and a ground) wire to a sub panel feed by a two pole 30 amp breaker..out of that you can run circuits for 220v or 110v..sub panels need to have the neutral bar isolated from the ground bar ( not bonded)...if ya need any help..let me know
jimbo9414 is offline Quote


Old 12-01-2015, 03:52 AM #5
rykus
Member

rykus's Avatar

Join Date: Sep 2015
Location: Under lights
Posts: 842
rykus is just really nicerykus is just really nicerykus is just really nicerykus is just really nicerykus is just really nicerykus is just really nicerykus is just really nicerykus is just really nicerykus is just really nicerykus is just really nicerykus is just really nice
I would pull 2/4 120 outlets from each side of the line in and try and be mindful of higher load items to spread draw as evenly as possible between the 2 hots.
rykus is offline Quote


Old 12-16-2015, 08:11 PM #6
Bwanabud
Senior Member

Bwanabud's Avatar

Join Date: Sep 2015
Location: Deep in the Timber
Posts: 1,572
Bwanabud is a splendid one to beholdBwanabud is a splendid one to beholdBwanabud is a splendid one to beholdBwanabud is a splendid one to beholdBwanabud is a splendid one to beholdBwanabud is a splendid one to beholdBwanabud is a splendid one to beholdBwanabud is a splendid one to beholdBwanabud is a splendid one to beholdBwanabud is a splendid one to beholdBwanabud is a splendid one to behold
Quote:
Originally Posted by jimbo9414 View Post
hi...retired electrician here....I would run a 10-3 (2 hots, neutral and a ground) wire to a sub panel feed by a two pole 30 amp breaker..out of that you can run circuits for 220v or 110v..sub panels need to have the neutral bar isolated from the ground bar ( not bonded)...if ya need any help..let me know
Almost all transformers have switched residential power over to 110/220...generally 208v.

Agree with this, and don't think the neutral & common are the same thing..they aren't. Be safe, growing isn't worth dying over.
Bwanabud is offline Quote


Post Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT +2. The time now is 03:24 PM.


Click to buy cannabis seeds at Ace Seeds


This site is for educational and entertainment purposes only.
You must be of legal age to view ICmag and participate here.
All postings are the responsibility of their authors.
Powered by: vBulletin Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.