grow room power
i want to design a 240v 30 amp circuit for a room i have because the house is wired with 15 amp 120/240v outlets.i want to know if i can put 2 1000w lights 8.4 amp total,T5 grow light .5 amp,2 inline fans 2 amps total and 2 ventilation fans 5 amps total on this new circuitt i want to build.so i have a total of 15.9 amps/16 amps on this circuit.is it safe to run all these appliances on the circuit without worries since it would be a 30 amp rated?
please and thank you |
|
|
|
|
|
#2 |
|
Overkill is under-rated.
Join Date: Jun 2009
Location: Norcal
Posts: 5,186
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Yes, as long as you keep the amp draw at or under 80% of the circuits rating for continuous duty use. The trick will be getting both 240v and 120v output from a 240v source. If you're good with wiring you can do it, if you don't know how I won't tell you.
__________________
*I'm fairly busy so please excuse my absence or slow responses to PM's! All about Growroom cooling: Keepin' it cool man (my 1st published article) How to automate reservoir top offs or most anything water-related The only UV-B lighting thread worth a damn CO2 for dummies ![]() Big grow: The 36KW medical/perpetual basement
|
|
|
|
|
|
#3 |
|
Newbie
Join Date: Sep 2015
Posts: 41
![]() |
You will be safe with 16 amps on a 30 amp circut. In growroom design area the sticky for "growroom electrical and wiring" has some good tip and pics to explain. If you don't understand please get professional help, peace of mind on electrical installations is priceless
|
|
|
|
|
|
#4 |
|
Newbie
Join Date: Nov 2015
Posts: 5
![]() |
hi...retired electrician here....I would run a 10-3 (2 hots, neutral and a ground) wire to a sub panel feed by a two pole 30 amp breaker..out of that you can run circuits for 220v or 110v..sub panels need to have the neutral bar isolated from the ground bar ( not bonded)...if ya need any help..let me know
|
|
|
|
|
|
#5 |
|
Member
Join Date: Sep 2015
Location: Under lights
Posts: 842
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
I would pull 2/4 120 outlets from each side of the line in and try and be mindful of higher load items to spread draw as evenly as possible between the 2 hots.
|
|
|
|
|
|
#6 | |
|
Senior Member
Join Date: Sep 2015
Location: Deep in the Timber
Posts: 1,572
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Quote:
Agree with this, and don't think the neutral & common are the same thing..they aren't. Be safe, growing isn't worth dying over. |
|
|
|
|
|
|
|
|