electrical concerns

3 months ago i set up a 4.5 x 9 tent running a 100w 6" vortex fan and 2 600w lights. also in the room i have a laptop and speakers.

everything was going fine until yesterday when the lights turned off unexpectedly. i checked and the outlets should be able to handle 1500w and i'm 200 shy of that on a single outlet. my roommates space heater runs 1500w and doesn't blow anything out in other rooms.

why is this happening? when i checked it out the ballasts were way hotter than usual and the surge protector and outlet were both also very hot, the outlet having evidence of melting/burning.

could it be that i live in a very old house and the wiring is about shot? there are only like 7 breakers for the entire house so i'm assuming most of these outlets are sharing one.

any input is appreciated.
__________________
Phil's good, man
pseudostelariae is offline Quote


Old 02-10-2014, 11:55 AM #2
pseudostelariae
Member

pseudostelariae's Avatar

Join Date: Oct 2007
Posts: 329
pseudostelariae will become famous soon enoughpseudostelariae will become famous soon enough
i just tried unplugging one of the 600s and it ran for about an hour before shutting off again. happens with 2 different surge protected outlet strips. how is it that all of a sudden this is a problem? i haven't changed anything. in fact, i used to run an additional 6" inline fan without any problem.
__________________
Phil's good, man
pseudostelariae is offline Quote


Old 02-10-2014, 12:58 PM #3
johndoe123
Guest

Posts: n/a
Space heaters use 1500 watts when they are on hi. Is there any way to run a drop cord from a lesser used circuit to your grow space? If you do just make sure you get one that is 10 gauge heavy duty. Also an amp clamp will help ya figure out your draw on different circuits. You should only be using 2/3 draw to what the breaker is rated for
Quote


1 members found this post helpful.
Old 02-10-2014, 01:21 PM #4
pseudostelariae
Member

pseudostelariae's Avatar

Join Date: Oct 2007
Posts: 329
pseudostelariae will become famous soon enoughpseudostelariae will become famous soon enough
thank you! yes, tomorrow i will be trying another cord from a far away outlet to split up the load in hopes that lights on happens without any problem. i'll have to pick up an amp clamp and see what's going on. if i can't get this figured out i'll either have to get an electrician and eat the cost or talk to the landlord. even though i'm OMMP and 100% legal, i'd rather fix this in-house...
__________________
Phil's good, man
pseudostelariae is offline Quote


Old 02-10-2014, 01:31 PM #5
Shovelhandle
Member

Join Date: Feb 2007
Location: Swan Town, Vt.
Posts: 130
Shovelhandle is a jewel in the roughShovelhandle is a jewel in the roughShovelhandle is a jewel in the roughShovelhandle is a jewel in the roughShovelhandle is a jewel in the roughShovelhandle is a jewel in the rough
You should use not more than 80% of the circuit rating. Is the circuit on a 15 or 20 amp breaker? Where is the interruption, the circuit breaker in the panelboard or one of the strips? What else goes out when the circuit trips? 10 AWG (american wire gauge) is not necessary on a 15 or 20 amp circuit unless one needs to run a very long distance. Use a heavy duty cord, 12 AWG for up to 2000W and 14 AWG for up to 1400 watts, just don't use any longer cord than you need. I run a little over 1000 watts of light plus fans on a new 20 amp circuit (new breaker, wire and receptacle). The ballasts do get hot (220ºF) this is normal. Do be very careful. Check for loose plug/receptacle connections. This can be dangerous but this usually won't cause the breaker to trip. Can you get an electrician to check it out? Maybe use the 1500w heater on your circuit and check the circuit breaker. A breaker should not be above 130º with a full load. A loose connection at the breaker, either the breaker into the panel stab or the wire terminal will cause high temperature that could trip the breaker. If the breaker is tripping under less than full load and there are no loose connection problems the breaker could be 'weak' and should be replaced. I'm not addressing possible arc faults as you mentioned the house wiring is old. Arc fault breakers are new technology and are required for just about all outlets in the home now. I'm an electrician and infrared thermographer and this is right up my alley. Unfortunately, we can't do much troubleshooting over the internet. Good luck, be careful.
Shovelhandle is offline Quote


Old 02-10-2014, 02:00 PM #6
pseudostelariae
Member

pseudostelariae's Avatar

Join Date: Oct 2007
Posts: 329
pseudostelariae will become famous soon enoughpseudostelariae will become famous soon enough
Quote:
Originally Posted by Shovelhandle View Post
You should use not more than 80% of the circuit rating. Is the circuit on a 15 or 20 amp breaker? Where is the interruption, the circuit breaker in the panelboard or one of the strips? What else goes out when the circuit trips? 10 AWG (american wire gauge) is not necessary on a 15 or 20 amp circuit unless one needs to run a very long distance. Use a heavy duty cord, 12 AWG for up to 2000W and 14 AWG for up to 1400 watts, just don't use any longer cord than you need. I run a little over 1000 watts of light plus fans on a new 20 amp circuit (new breaker, wire and receptacle). The ballasts do get hot (220ºF) this is normal. Do be very careful. Check for loose plug/receptacle connections. This can be dangerous but this usually won't cause the breaker to trip. Can you get an electrician to check it out? Maybe use the 1500w heater on your circuit and check the circuit breaker. A breaker should not be above 130º with a full load. A loose connection at the breaker, either the breaker into the panel stab or the wire terminal will cause high temperature that could trip the breaker. If the breaker is tripping under less than full load and there are no loose connection problems the breaker could be 'weak' and should be replaced. I'm not addressing possible arc faults as you mentioned the house wiring is old. Arc fault breakers are new technology and are required for just about all outlets in the home now. I'm an electrician and infrared thermographer and this is right up my alley. Unfortunately, we can't do much troubleshooting over the internet. Good luck, be careful.
thanks for the input! i just checked the outlet and it is indeed very loose. i can almost pull it out of the wall. in fact a few of them are. i feel like an idiot i didn't notice this already. when i initially set everything up i made sure it was running full blast just in case i ever had to run both fans and it worked fine, plugged in the space heater to see what would happen and it was a blackout. breaker didn't trip but surge protectors did. i figured that meant since i wasn't running a full load with just the tent, i'd be fine so long as i avoided any additional electronics.

when the lights go out, the surge protector on the power strip does its thing while the CFL plugged into the other outlet stays on. the breaker isn't tripping whatsoever and the other outlets in the room are unaffected. apparently i AM running too much power in this room so i will be diverting from other outlets and will do my best to find cords that are long/heavy duty enough without excessive length.

right now everything is unplugged and the plants are having an early bedtime. since nothing on the circuit breaker is labeled, would it be wise to flip them until i find which cuts power to my room and then look and possibly tighten things up? obviously i have no idea what i'm doing and the closest i can get to an electrician without either going around the landlord and calling one or just getting her involved is another roommate who briefly worked under a licensed electrician. i'll see what he has to say a little later in the morning.
__________________
Phil's good, man
pseudostelariae is offline Quote


Old 02-10-2014, 03:11 PM #7
johndoe123
Guest

Posts: n/a
Quote:
Originally Posted by Shovelhandle View Post
You should use not more than 80% of the circuit rating. Is the circuit on a 15 or 20 amp breaker? Where is the interruption, the circuit breaker in the panelboard or one of the strips? What else goes out when the circuit trips? 10 AWG (american wire gauge) is not necessary on a 15 or 20 amp circuit unless one needs to run a very long distance. Use a heavy duty cord, 12 AWG for up to 2000W and 14 AWG for up to 1400 watts, just don't use any longer cord than you need. I run a little over 1000 watts of light plus fans on a new 20 amp circuit (new breaker, wire and receptacle). The ballasts do get hot (220ºF) this is normal. Do be very careful. Check for loose plug/receptacle connections. This can be dangerous but this usually won't cause the breaker to trip. Can you get an electrician to check it out? Maybe use the 1500w heater on your circuit and check the circuit breaker. A breaker should not be above 130º with a full load. A loose connection at the breaker, either the breaker into the panel stab or the wire terminal will cause high temperature that could trip the breaker. If the breaker is tripping under less than full load and there are no loose connection problems the breaker could be 'weak' and should be replaced. I'm not addressing possible arc faults as you mentioned the house wiring is old. Arc fault breakers are new technology and are required for just about all outlets in the home now. I'm an electrician and infrared thermographer and this is right up my alley. Unfortunately, we can't do much troubleshooting over the internet. Good luck, be careful.
Listen to this guy I am a bricklayer by trade My advice was not very far off though. I always try to err on the side of caution when it comes to electricity
Quote


Old 02-10-2014, 07:19 PM #8
rives
Inveterate Tinkerer


rives's Avatar

Join Date: Feb 2010
Posts: 6,090
rives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant future
When Shovelhandle mentioned the receptacle being loose, he was not talking about how the receptacle was mounted in the wall, he was talking about the wires being loose in the back of the receptacle. Many cheap receptacles just use a push-in, spring-loaded arrangement to terminate the wires. These should be changed out to "commercial" or "specification" grade components which use screws to make the connection. Also, make sure that the receptacles are not worn out - it should take some effort to insert the plug, and the plug should stay tight to the wall rather than sagging down from the weight of the cord.
rives is offline Quote


3 members found this post helpful.
Old 02-12-2014, 11:46 AM #9
Shovelhandle
Member

Join Date: Feb 2007
Location: Swan Town, Vt.
Posts: 130
Shovelhandle is a jewel in the roughShovelhandle is a jewel in the roughShovelhandle is a jewel in the roughShovelhandle is a jewel in the roughShovelhandle is a jewel in the roughShovelhandle is a jewel in the rough
Quote:
Originally Posted by rives View Post
When Shovelhandle mentioned the receptacle being loose, he was not talking about how the receptacle was mounted in the wall, he was talking about the wires being loose in the back of the receptacle. Many cheap receptacles just use a push-in, spring-loaded arrangement to terminate the wires. These should be changed out to "commercial" or "specification" grade components which use screws to make the connection. Also, make sure that the receptacles are not worn out - it should take some effort to insert the plug, and the plug should stay tight to the wall rather than sagging down from the weight of the cord.
Yut, that's it. The wires must be tight and the receptacle must grab the plug firmly. There is a tool an electrician can use to measure the pull-out force but It's not commonly used, you can tell pretty much if it's tight or loose. I have an infrared imaging camera and I've checked out my grow equipment for excessive heating. I was not comfortable with (2) 400 watt HPS on one timer, not to mention the fans and air pump so I run two timers set the same. I have the (2) 400 watt HIDs, a 216 watt T-5HO fixture, a box fan, an exhaust fan all running on one 20 amp circuit with no issues. No heating ant the recepticles, the wiring or the breaker. All this load is less than 10 amps or 50% of capacity.
Shovelhandle is offline Quote


1 members found this post helpful.
Old 02-12-2014, 03:35 PM #10
Jhhnn
Senior Member

Join Date: Jan 2013
Location: Denver CO
Posts: 4,949
Jhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant futureJhhnn has a brilliant future
Quote:
Originally Posted by rives View Post
When Shovelhandle mentioned the receptacle being loose, he was not talking about how the receptacle was mounted in the wall, he was talking about the wires being loose in the back of the receptacle. Many cheap receptacles just use a push-in, spring-loaded arrangement to terminate the wires. These should be changed out to "commercial" or "specification" grade components which use screws to make the connection. Also, make sure that the receptacles are not worn out - it should take some effort to insert the plug, and the plug should stay tight to the wall rather than sagging down from the weight of the cord.
Indeed. Your advice is always excellent. The high continuous current draw of grow equipment will bring out any weaknesses in the house wiring.

The described symptoms seem exactly like the usual low voltage/ high current over heating situation caused by a faulty connection. I'd start with an inspection/ new receptacle at the outlet box, work from there. Unfortunately, there's a pretty steep learning curve for people not familiar with the hardware & some tricky situations around aluminum wiring, too.

One of the smartest things growers can do is to inspect/ upgrade stuff like that before they start growing, take care of it or call in an electrician before he has to beat his way through the plants.
Jhhnn is offline Quote


Post Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT +2. The time now is 03:25 PM.


Click to Visit Greenpoint Seeds


This site is for educational and entertainment purposes only.
You must be of legal age to view ICmag and participate here.
All postings are the responsibility of their authors.
Powered by: vBulletin Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.