Wiring help
Hello everybody
I needing to upgrade some wiring in my house to upgrade to a 1000w light. Currently I have maxed out the circuit I'm currently on. I would like to run a new breaker 30amps which i would like to run to 2 receptacle. 15 amps to each receptacle. Which should give me plenty of power for my whole room. My question is should i run 2 wires of 10g romex from the breaker or it is safe with 1 wire running to both receptacles? I was planing on using romex 10/3 wiring. Thanks in advance Much love |
|
|
|
|
|
#2 |
|
Senior Member
Join Date: Nov 2009
Posts: 1,012
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
You will wat to move this to grow room design and equipment forums to have a sparky there to help you..
IM no electrician but imo you may be overkilling but dont know what your room draws. As a rule of thumb you dont want to draw more then 75-80 % of effective load on circuit. I have a 1K which I run on a a dedicated 15 amp line ( 1K draws 10 amps, 75% of 15 amp max) using 14/2 romex. Then I have another line which is 20 amps with 12/2 romex. This runs the exhaust ( 3-4 amps give or take) a space heater in winter ( 5-6 amps give or take) and miscellaneous fans, an auxillary outlet ( for cleaning or whatever) and that pretty much takes care of it. If you are running hydro with pumps etc. ( I dont) then you will need to add the amps of what they draw up and figure it out yourself. You will probably need to provide more info on what your setup is and draws but from what I see right now you may be a little overkill on the 30 amp... Also dont know how many open slots you have in your panel. Btw.. the bigger gauge wire i.e 10/3 the more pain in the ass is it is to work with. Also just because you run 30 amp capacity with approp. wire doesnt mean you can use 15 amp receptacles. You will need to use 30 amp outlets and receptacles to be code and they can get expensive and a PIA.. If you have room in your box just run your 1k off a dedicated 15 amp 14/2 line. That takes care of the meat and you can figure out what else you need for the gravy |
|
|
|
|
|
#3 |
|
Newbie
Join Date: Jan 2014
Posts: 6
![]() |
I might be going a little over kill.
To be honest i been reading lot about wire safety and i have completely scarred the fuck out of myself. I currently have 1 400w & 1 600w running in my veg area but i need to get my flower area going. So I'm adding a 1000w light. it pulls 9.4amps so total i think I'm would be around 20amps i figured 10amps would be plenty of extra for 2 or 3 fans. For receptacles i was wanting to use standard 15 amp receptacles but use 2 giving me 4 total plugs. Thanks for the help man. Also if a mod could move this to the right area i would be extremely apperceive. |
|
|
|
|
|
#4 |
|
Newbie
Join Date: Jan 2014
Posts: 6
![]() |
maybe running 2 15 amp breakers would be easier?
I only have to run about 20 feet of cable and its fairly easy from where the box and room are located. |
|
|
|
|
|
#5 |
|
Member
Join Date: Jan 2014
Location: The mistake on the lake!!!
Posts: 172
![]() ![]() |
There are a few ways to do this...personally I would give your room its own subpanel.. Providing you have room in your main. And you own or will be living there for a long time. I wouldn't think you need more than a 60amp 2 pole breaker in the main. Run 6awg to your sub panel from main (put it next to main to save on wire cost. Then run your new wiring to that and you will be golden. Also easier to isolate your grow. Don't forget to turn off your main panel before installing the breaker...I did that once.....once
|
|
|
|
|
|
#6 |
|
Inveterate Tinkerer
![]() ![]() Join Date: Feb 2010
Posts: 6,090
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
The first thing that you need to understand when doing electrical design is that the circuit breaker HAS to be/match the lightest-rated component in the circuit. If you were to use a 30 amp breaker, then all 30 amps could be applied to just one of your 15 amp receptacles even though there are several hooked to the circuit. Good things would not follow.
Your second idea about using (2) 15a breakers is the correct way to go about it. This provides the correct protection for the downstream components, with commonly used plug configurations. If you are up for a little more work, the sub-panel idea that Phat presented gives you the most flexibility for future expansion and change. You can also have more numerous dedicated circuits, provide individualized protection to certain types of components, have better protection, etc, etc. |
|
|
|
|
|
#7 |
|
Member
Join Date: Jan 2014
Location: The mistake on the lake!!!
Posts: 172
![]() ![]() |
If you need a little more info on installing a sub panel u can always shoot me a pm and I will Rey to give you a step thru...watch some YouTube bids on it to give you a rough idea of what you want...
|
|
|
|
|
|
#8 |
|
Newbie
Join Date: Jan 2014
Posts: 6
![]() |
Thanks for the feed back guys!!
I truly appreciate it. This stuff has been stressing me out hardcore. I don't have the option of running a sub panel but i do have a few open spots in my box. So 2 15amp beakers with romex 10/3 wire would be fine right? How this look for a parts list? https://www.homedepot.com/p/Eaton-15-...1515/100130719 https://www.homedepot.com/p/Southwire...8478/203424769 https://www.homedepot.com/p/Cooper-Wi...50WS/203595341 Or should i maybe just go ahead and run 20amp? I would not cost much more... Also I'm having a buddy help me with the wiring but i told him i would take the time to learn what i could so I'm not just having him do it for me. |
|
|
|
|
|
#9 | |
|
Member
Join Date: Jan 2014
Location: The mistake on the lake!!!
Posts: 172
![]() ![]() |
Quote:
|
|
|
|
|
|
|
#10 |
|
Inveterate Tinkerer
![]() ![]() Join Date: Feb 2010
Posts: 6,090
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
#10 wire is way overkill for a 15a circuit, and will make terminating the receptacle difficult. Unless your a very long distance from the panel, #14 is good for 15a and #12 for 20a. I prefer to run a minimum of #12, but it is more than required.
|
|
|
|
|
|
|
|