electrical question
I have a 30 amp dedicated circuit to my grow space with 10/2 wiring
Off of this circuit I want to run these items: 2-600w ballasts on 1-intermatic timer 2-can fans for filters 1-8 port air pump 2-small air pumps with 2 hose outlets each 2-2' cfl tube lights at probably 30w each max 1-636 gph pump 1-1/4hp water chiller will that be too much? If so, I have an additional identical circuit that COULD (with quite a bit of work) be used to power some of those items. However, I already have a in wall a/c unit running on that circuit. advice? additional question: can 1 intermatic mechanical timer run a recepticle which has 2-600w ballasts plugged into it? |
|
|
|
|
|
#2 |
|
Banned
Join Date: May 2009
Location: 209...Prop 215 Med
Posts: 701
![]() ![]() ![]() ![]() ![]() ![]() |
you should be fine, only thing im not sure of is the how many amps are pulled with a 1/4 chiller. if its only a couple then your good.
2nd question. yes it can 2 600w only pull 10-12 amps. you just want to get a 20amp receptacle. |
|
|
1 members found this post helpful. |
|
|
#3 |
|
Member
Join Date: Jul 2011
Posts: 180
![]() ![]() |
here's some info from aqua cave
* Capable of Chilling: 170 gallons - 10° F; 100 gallons - 30° F * 480 Watt * 120/60 V/HZ * 4 Amps other websites state 4 amps as well. Every receptacle in the room is 20 amp. |
|
|
|
|
|
#4 |
|
Inveterate Tinkerer
![]() ![]() Join Date: Feb 2010
Posts: 6,090
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
You do not want to run 20 amp receptacles on a 30 amp circuit. You could build a small distribution center with 15 or 20 amp breakers and feed it from the 30 amp circuit, and the load would probably be fine. It is too much for a 20 amp circuit - with ballast losses figured on the lights plus the chiller, you are already at 1800 watts (15 amps). The 80% rule states that you are only allowed to run 80% of the breaker rating for continuous loads (defined as any load over 3 hours in duration).
If you are talking about the Intermatic T-101, 103 family of timers, then yes, they can easily handle (2) 600s. If you are talking about the plug-in style, then no. |
|
|
1 members found this post helpful. |
|
|
#5 | |
|
Member
Join Date: Jul 2011
Posts: 180
![]() ![]() |
Quote:
when you say I am at 80%/15 amps, you are basing that on a 20 amp circuit, right? how do you figure 1800 watts? 600w + 600w + 480w = 1680w I thought 80% of 2400 amps (derived from 20 amps @ 120 volts) is 1920 watts? Is my math correct? Probably not, that's why I'm here asking you. The timer is the t101r so that's good. How do I find the amount of watts consumed by a pump? My smaller pumps I can figure out from a website off petco but the larger pump has no brand indication. Is there a tool or something I can plug the pump or other appliances into in order to measure this figure? Thanks for your help. I see your posts everywhere and you seem to know your stuff...and then some. edit* If the distribution center is a subpanel, what can I run off of that box? Total # of breakers at 20 and/or 15 amp and total # of watts. Thanks again. |
|
|
|
|
|
|
#6 | ||||
|
Inveterate Tinkerer
![]() ![]() Join Date: Feb 2010
Posts: 6,090
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Quote:
Quote:
As far as the 1800 watts, I was estimating & including the ballast losses. The 600w rating is a nominal rating, and is for the lamp only. The ballasts themselves take power to operate, and depending on the ballast this can be another 5%-15%. I was assuming 10%, so that adds another 120 watts to the load, for a total of 1800 watts. Your math is correct. My point was that with just the lights and the chiller, you are already at 1800 watts and you had a whole string of additional equipment that you wanted to run. Quote:
Quote:
Each individual 15 amp breaker could handle 1800 watts of intermittent load or 1440 watts of continuous load, and the 20 amp breakers could have 2400 watts of intermittent load or 1920 watts of continuous load. For instance, you could put each of your lights on their own dedicated 15a breaker, the chiller on it's own 15a breaker, and the rest of the gear on another 15a breaker. As long as you keep your total connected load within the limits of the 30a breaker, you're fine. I know this gets confusing. If this isn't clear, ask away! |
||||
|
|
2 members found this post helpful. |
|
|
#7 |
|
Member
Join Date: Jul 2011
Posts: 180
![]() ![]() |
Rives: I love the detailed response. You umm, rock.
I picked up a killawatt on my way home from work today. I just want to get one last thing straight: me putting 2-20 amp receptacles on a 30 amp circuit would do what exactly? I am NOT going to use it, I'm just curious as to worst case scenario and likely scenario. Thanks. |
|
|
|
|
|
#8 |
|
Banned
Join Date: Mar 2012
Posts: 2,614
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
When equated to water:
Voltage is like the size of your water pipe. Amperage is like the force behind the water. If your amperage is too high, it will blow your "water pipe". AKA, it will overload yo. Hope this helps. |
|
|
|
|
|
#9 |
|
Member
Join Date: May 2009
Location: so cal
Posts: 920
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
baba-booey, baba-booey, Howard Sterns penis....
__________________
.. but was I butt naked blasting tane inside fuck NOOOOOOOO! god damn--- midwestHIGHS all hydro systems boil down to two things imo, 1) the system!!! 2) the operator!!! And one ain't worth a plug nickel without the other... BigToke My current grow Super Sour Berry 47 bio bucket style : www.icmag.com/ic/showthread.php?t=338573 A sad state of affairs. A crippled America. A pipe dream buttfucked. Immune. Stronger than all. A lament for a rookie officer, punk ass weak little lamb. For the mob, truly, does rule at this particular time. We've grown into a monster. An arrogant, explosive motherfuck. Hard as a rock. Shut like a lock. Pantera |
|
|
1 members found this post helpful. |
|
|
#10 | |
|
Inveterate Tinkerer
![]() ![]() Join Date: Feb 2010
Posts: 6,090
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Quote:
Additionally, there is a time/current curve that determines how quickly the breaker will respond. A brand new, completely in spec breaker can take 500 seconds to trip at 150% loading, and 100 seconds at 200% loading. So, you could easily put 60 amps through one of your 20 amp rated receptacles for nearly 2 minutes if your breaker met brand-new specifications. Great recipe for a fire.
__________________
Philips 315w CDM Elite (CMH) - Overview & Information My DIY Hybrid LED/PL-L Luminaire The VolksLED - DIY LEDs for the Masses Last edited by rives; 03-12-2013 at 01:58 AM.. |
|
|
|
|
|
|
|
|