| Forums > Marijuana Growing > Growroom Designs & Equipment > Growroom Lighting > How much air to cool 6kw of light. | ||
| How much air to cool 6kw of light. | Thread Tools | Search this Thread |
|
|
#1 |
|
Guest
Posts: n/a
|
How much air to cool 6kw of light.
I have a friend that is trying to setup a 6 - 1kw setup in a 10x12 room. He is using some eurogrowers and is in a commercial building. He has a large building and can pretty much cut holes in whatever. How much air would it take and how should he setup his room and reflectors to air cool his reflectors and the room?
BTW, he also mentioned he wants to do it the cheapest way possible, lol. |
|
|
|
|
#2 |
|
Guest
Posts: n/a
|
I use 63,000 btu in a 15x 15 room with almost 11,000 watts. Thats over 5 tons of cooling and 2 swamp coolers to help moisten the dry air from the 2 AC units. I run a sealed room with split unit type ac units that don't exhaust any air. I use a large co2 generator with lp gas so that adds heat.
So i think 30,000 btu or a Large window unit or 3 each 12,00 btu portable units would work. MOD |
|
|
|
|
#3 |
|
Guest
Posts: n/a
|
Thanks, but what I was looking for was how big of a centrifugal fan in cfm would i need to actively vent the room with to keep it at a manageable growing temperature?
Without a/c. |
|
|
|
|
#4 |
|
Member
Join Date: Feb 2006
Posts: 207
![]() |
wothout a/c?
a shitload i think one 6 " vortex 440 cfm will cool two 1k hps but i think your friend should seriously consider the a/c's |
|
|
|
|
|
#5 |
|
Member
Join Date: Mar 2006
Posts: 131
![]() |
200 cfm per One thousand watt hps/mh.
You need a fan for 6 - 1k watts 10" Fantech FKD Inline Fan w/cord - 1266 cfm
__________________
If it wasn't for the Grandaddy smokin!! You know what I mean fo sho.. Last edited by HYDRO KING; 03-25-2006 at 02:30 AM.. |
|
|
|
|
|
#6 |
|
Tiger, Tiger, burning bright...
Join Date: May 2005
Posts: 4,256
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Cool tubed 1kw lights can be effectively cooled with 100 CFM, depending on the effeciency of your ducting. Given the backpressure most growers create in thier systems, I'd go 250 CFM, just to be sure.
Air conditioning is generally calculated with 3500 BTU per 1kw light. Basically just restating the good information you've already been given in simpler terms.
__________________
Remember - Every 'elite' started off as someone's bagseed kingjobber - This hash just uncentered my chi Growing cannabis is only as complicated and expensive as you want it to be. Current Grow: Knowledge Guides: Diatomaceous Earth - The Best Pesticide You've Never Heard Of Pontiac's DIY Link-O-Rama Unofficial Glossary for New Growers The Water Cure- How, when, and why How to remove 'HPS Orange' quick and easy! |
|
|
|
|
|
#7 |
|
New Member
Join Date: Apr 2006
Posts: 22
![]() |
Without AC or cooled hoods...a 1200+ CFM blower. Ideally, you'll be pulling/pushing thru two CAN100 sized filters, plus(not so ideally) some length of ducting. So you end up moving a lot less than the rated 1200+...but should be ok until outside temps get around 27-30*C or higher.
Last edited by whoamI?whoRu!; 04-05-2006 at 11:44 PM.. |
|
|
|
|
|
#8 |
|
POTHEAD
Join Date: Sep 2005
Location: the magical forest of marijuana
Posts: 556
![]() ![]() |
[quote=NiteTiger]
Air conditioning is generally calculated with 3500 BTU per 1kw light. QUOTE] what if the 1kw light is inside a cooltube? thanks.
__________________
medical marijuana patient/caregiver in compliance with CA. Prop. 215. Round 1 OG Kush: BioTubs: Harvested Round 2 OG Kush: BioBuckets: Failure Round 3+4 Soil OG kush, Blueberry kush, Grapefruit: Watch Me Grow the Dank! “This country, with its institutions, belongs to the people who inhabit it. Whenever they shall grow weary of the existing government, they can exercise their constitutional right of amending it, or their revolutionary right to dismember or overthrow it.” Abraham Lincoln First Inaugural Address |
|
|
|
|
|
#9 |
|
Member
Join Date: Feb 2006
Posts: 35
![]() |
Chodo do a 10" or 12" vortex, it'll take care of your heat issues if they are used with cool tube reflectors!!
|
|
|
|
|
|
#10 |
|
Member
Join Date: Aug 2004
Location: None of ya business ya nosy bugger!
Posts: 468
![]() |
Chodo if you got a minute read these cached OG links from R2k aka ranger2000. His ventilation knowledge never steered me in the wrong direction.
There a simple formula he uses/devised and this thread has all the information you should need in these 2 pages.... https://72.14.207.104/search?q=cache:...k&ct=clnk&cd=1 https://66.249.93.104/search?q=cache:...k&ct=clnk&cd=2 |
|
|
|
|
|
|
|