Wiring High Heat Shut Off for 100 Amp sub panel.

I'm looking for advice on how to wire a high heat shut off into a 16k flower room. The wiring works such that a 100 amp contactor is tripped by a intermatic t103. This feeds a 100amp sub panel which controls my lights. The timer is run directly from the main panel. Would hate for my ac's to die on me without this wired in.

Necessary equipment and a wiring diagram would be immensely appreciated.
D-Note is offline Quote


Old 10-07-2012, 05:00 AM #2
deacon1503
Member

Join Date: May 2010
Location: Lower Peninsula
Posts: 62
deacon1503 will become famous soon enoughdeacon1503 will become famous soon enough
I'm sure plenty of.guys in here can answer this but I know Olyver on the Farm can. u could plug ur contractor trigger wire into a high temp shutoff thats in the room?
deacon1503 is offline Quote


Old 10-07-2012, 05:02 AM #3
DocCrow
Member

DocCrow's Avatar

Join Date: Sep 2012
Location: Mid World
Posts: 197
DocCrow will become famous soon enoughDocCrow will become famous soon enough
show me some pics of what you have and I will show you what you need and how to wire it so the lights go out if it gets too hot and come back on when temps drop to safe zone. I was an electrician.FWIW

DC
__________________
“Freedom is something that dies unless it's used” -Hunter S Thompson

My cabinet design and build https://www.icmag.com/ic/showthread.php?t=246458

Doc Crow's Medicine Cabinet: A Perpetual PPK Micro SOG https://www.icmag.com/ic/showthread.php?t=248868
DocCrow is offline Quote


Old 10-07-2012, 05:19 AM #4
PoopyTeaBags
State Liscensed Care Giver/Patient, Assistant Trailer Park Supervisor

PoopyTeaBags's Avatar

Join Date: Apr 2009
Location: Man-Whorin' for Cheeseburgers
Posts: 4,875
PoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud of
Quote:
Originally Posted by D-Note View Post
I'm looking for advice on how to wire a high heat shut off into a 16k flower room. The wiring works such that a 100 amp contactor is tripped by a intermatic t103. This feeds a 100amp sub panel which controls my lights. The timer is run directly from the main panel. Would hate for my ac's to die on me without this wired in.

Necessary equipment and a wiring diagram would be immensely appreciated.

umm im no electrictian but i think you doing it wrong...

if your doing a high heat shut off you need an digital thermoter that can be hooked up to a switch that will shut off the plugs.. i guess you could do the breaker but thats pointless as on the plugs you can install a restart function that starts the plugs back up...

and why would you want to shut off all 16k wouldnt you want to just shut off half???
__________________


Poopy teabags Soma and Grindhouse
*Completed*

Prophets actually get flowered out *Completed*
https://www.icmag.com/ic/showthread.php?t=180811

LVPK and Reclining Buddha RDWC
https://www.icmag.com/ic/showthread.php?t=199088

BAAAAM! Peanut Butter & JAAAAM!
PoopyTeaBags is offline Quote


Old 10-07-2012, 05:35 AM #5
rives
Inveterate Tinkerer


rives's Avatar

Join Date: Feb 2010
Posts: 6,090
rives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant future
There are a lot of ways to go about doing this, it depends on what you are wanting to protect against and how you feel it is to best deal with it. Do you want it incorporated with smoke detection, is your a-c always capable of handling the heat load (at least if it is functional), etc. As PTB pointed out, you can start by feathering out some of your lighting and progressively dump more if the things don't cool down. You can dump the whole works and bring it back on as Doc mentioned, or you can have it latch out so that it needs to be manually reset. It all depends on what you want, how near you are to your grow, how often you visit, etc.

I'm setting up my new system to where it will dial back the wattage on the ballasts, if that doesn't do it then it will dump sections of lighting, and if that doesn't take care of things all of the lights go out. If a smoke detector trips, a shunt-trip breaker kills the whole thing.
rives is offline Quote


Old 10-07-2012, 06:12 AM #6
deacon1503
Member

Join Date: May 2010
Location: Lower Peninsula
Posts: 62
deacon1503 will become famous soon enoughdeacon1503 will become famous soon enough
Quote:
Originally Posted by rives View Post
There are a lot of ways to go about doing this, it depends on what you are wanting to protect against and how you feel it is to best deal with it. Do you want it incorporated with smoke detection, is your a-c always capable of handling the heat load (at least if it is functional), etc. As PTB pointed out, you can start by feathering out some of your lighting and progressively dump more if the things don't cool down. You can dump the whole works and bring it back on as Doc mentioned, or you can have it latch out so that it needs to be manually reset. It all depends on what you want, how near you are to your grow, how often you visit, etc.

I'm setting up my new system to where it will dial back the wattage on the ballasts, if that doesn't do it then it will dump sections of lighting, and if that doesn't take care of things all of the lights go out. If a smoke detector trips, a shunt-trip breaker kills the whole thing.
I like that!
deacon1503 is offline Quote


Old 10-07-2012, 06:42 AM #7
TribalSeeds
Guest

Posts: n/a
Quote:
Originally Posted by rives View Post
There are a lot of ways to go about doing this, it depends on what you are wanting to protect against and how you feel it is to best deal with it. Do you want it incorporated with smoke detection, is your a-c always capable of handling the heat load (at least if it is functional), etc. As PTB pointed out, you can start by feathering out some of your lighting and progressively dump more if the things don't cool down. You can dump the whole works and bring it back on as Doc mentioned, or you can have it latch out so that it needs to be manually reset. It all depends on what you want, how near you are to your grow, how often you visit, etc.

I'm setting up my new system to where it will dial back the wattage on the ballasts, if that doesn't do it then it will dump sections of lighting, and if that doesn't take care of things all of the lights go out. If a smoke detector trips, a shunt-trip breaker kills the whole thing.
Can you explain the smoke detector setup?
Quote


Old 10-07-2012, 06:45 AM #8
PoopyTeaBags
State Liscensed Care Giver/Patient, Assistant Trailer Park Supervisor

PoopyTeaBags's Avatar

Join Date: Apr 2009
Location: Man-Whorin' for Cheeseburgers
Posts: 4,875
PoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud ofPoopyTeaBags has much to be proud of
Quote:
Originally Posted by TribalSeeds View Post
Can you explain the smoke detector setup?


my guess is the smoke detectors are hardwired to the box and will trip if they go off...
__________________


Poopy teabags Soma and Grindhouse
*Completed*

Prophets actually get flowered out *Completed*
https://www.icmag.com/ic/showthread.php?t=180811

LVPK and Reclining Buddha RDWC
https://www.icmag.com/ic/showthread.php?t=199088

BAAAAM! Peanut Butter & JAAAAM!
PoopyTeaBags is offline Quote


Old 10-07-2012, 07:09 AM #9
rives
Inveterate Tinkerer


rives's Avatar

Join Date: Feb 2010
Posts: 6,090
rives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant futurerives has a brilliant future
Quote:
Originally Posted by TribalSeeds View Post
Can you explain the smoke detector setup?
You can buy smoke detectors that just have an output relay whose contacts are closed upon activation. A shunt trip is a device that attaches to a breaker and trips it when a voltage is applied to it. I'm crunching the logic with an Allen-Bradley Micro plc.


Shunt trip - https://www.automationdirect.com/adc/...ries/WMZTST110

Breaker used with it - https://www.automationdirect.com/adc/...xx%29/WMZT2C10
rives is offline Quote


1 members found this post helpful.
Old 10-07-2012, 07:20 AM #10
DocCrow
Member

DocCrow's Avatar

Join Date: Sep 2012
Location: Mid World
Posts: 197
DocCrow will become famous soon enoughDocCrow will become famous soon enough
Hardwired smoke detectors are all set up to be interconnected. They have a 3rd wire on them that, once triggered, sends a signal to the rest so they go off too. You could hook up the signal wire to a Normally Closed relay so it kills the power if the detector goes off.

EDIT: looks like Rivers beat me to the punch. I would just hook it up to a normally closed relay so it kills the lighting contactor.
__________________
“Freedom is something that dies unless it's used” -Hunter S Thompson

My cabinet design and build https://www.icmag.com/ic/showthread.php?t=246458

Doc Crow's Medicine Cabinet: A Perpetual PPK Micro SOG https://www.icmag.com/ic/showthread.php?t=248868
DocCrow is offline Quote


1 members found this post helpful.

Post Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT +2. The time now is 03:25 PM.


Click to shop for Extractors and Hardware


This site is for educational and entertainment purposes only.
You must be of legal age to view ICmag and participate here.
All postings are the responsibility of their authors.
Powered by: vBulletin Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.