#1 |
|
PROFESSIONAL SURVIVOR
Join Date: Jun 2011
Location: In your head
Posts: 326
![]() ![]() ![]() |
Ok, so I keep tripping the breaker in my garage. I'm overloaded obviously. The only think I know about electricity is that if your not careful, it causes you pain and a possibility of death. With that said, I need some advice.
I have a total of 72.19 actual amps being pulled from my grow equipment alone. These numbers are ascertained form the labels and some quick math on 3 1k HPS/MH lights. I'm guessing that the line will probably have to be at least 100 feet into the grow room. 1. Should I just throw a couple of 50 amp breakers in the box out in the garage and run the two new lines into the grow room? Then just split up the power draw evenly as possible? OR 2. Should I run a single line from the garage into a sub panel located in the grow room? Which is cheaper? What wire gauge is needed? This is about all I know right now. I will answer questions as they are asked of me. I'm open for debate and suggestions from all. You guys are the best. Thank you so much for all your help. Peace.
|
|
|
|
|
|
#2 |
|
Member
Join Date: Oct 2009
Posts: 459
![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Man, you need to talk to Rives (https://www.icmag.com/ic/member.php?u=136396).
He's given the best electrical advice I've seen on these forums. Good luck and....don't die! |
|
|
3 members found this post helpful. |
|
|
#3 |
|
Member
Join Date: Sep 2007
Posts: 818
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
A sub panel would be for the best. Or you could run 5-20 amp circuits on 12 gauge wire.
|
|
|
1 members found this post helpful. |
|
|
#4 |
|
PROFESSIONAL SURVIVOR
Join Date: Jun 2011
Location: In your head
Posts: 326
![]() ![]() ![]() |
thus far a sub panel would be easier I think. I'm going to need at least two 50 amp lines for sure. I just landed an air pump for my res that draws 4.2 amps alone lol. I haven't got to talk with Rives yet as I have been busy. Thanks for the input man!
|
|
|
|
|
|
#5 | ||
|
Senior Member
![]() Join Date: Mar 2010
Posts: 3,025
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
imo you wanna run close to 80 amps you need a 100 amp sub panel, then in the 100amp sub panel you can divide all the power loads evenly so no single breaker is overloaded
couldnt tell you what each breaker should be cuz i dont know your setup, but you need a 100 amp sub panel. i would go for option 2 and run one single line to a 100 amp sub panel to the grow... why do you draw so much power? is everything running on 120v? i run 7 tons of A/C and 15 lights and dont go over 48 amps...ofcourse i have everything on relays... but yes rives and iron lion arethe 2 best sparkys we have here imo, they can give you better info
__________________
FRESH BEANS Co.(COMMING THIS SUMMER) Quote:
Quote:
Phytophythora - "The Plant Destroyer" Pythium Root Rot in Soil and Hydroponic Applications Salt Tolerance of Plants in Soil Pour Thru Method for testing soil PH and EC Substrate pH: Getting it Right for Your Crops Marijuana Documentaries |
||
|
|
1 members found this post helpful. |
|
|
#6 |
|
Inveterate Tinkerer
![]() ![]() Join Date: Feb 2010
Posts: 6,090
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
As the posts above said, you would probably be better off with a dedicated sub-panel. However, I think the best place to start would be to see how much of your equipment you can convert from 120v to 240. You may not be aware of it, but equipment draws half the amperage at 240v then it does at 120, though the wattage remains constant. If you are only running 3k, it is hard for me to imagine how you got to 72 amps. At that rate, you are already close to full capacity on a 100 amp panel (as Joe alluded to, you only want to run at 80% of the breaker capacity for a continuous load, which is defined as anything that runs over 3 hours at a time).
Many sub-panels have 125 amp buswork and cost about the same as the 100 amp models, so you could go that route and have a little room to expand into. Be aware that if this panel is to be fed from a sub-panel in your garage, it is unlikely that you have enough power to that point to carry this much additional power to your growroom sub-panel - it would probably have to be fed from the main panel. To the above posters - thanks for the kind words! |
|
|
6 members found this post helpful. |
|
|
#7 |
|
Certified Bloomin' Idiot
Join Date: Jul 2004
Posts: 1,741
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Ya'all take care and beware when overloading circuits, especially in ones dwelling, waking up dead really,really sucks...it's been known to ruin ones whole day.
![]() I believe a 1000 watt copper coil ballast eats about 10,,,11 amps on 120, half that @ 240 volts, if I do recall correctly. Note: A 220 volt circuit is a three wire circuit with two hot wires and a shared neutral (white) wire so that there would be 27 amps on each hot wire for a total of 27 amps at 220 volts. IMB ![]() Basic Princples of Electricity https://www.icmag.com/ic/showthread.php?t=16384 “ Electrical Safety for Indoor Grows,” https://www.icmag.com/ic/showthread.php?t=15468 Extension Cord Safety https://www.icmag.com/ic/showthread.php?t=40988 Electrocution prevention w/ GFCI's (Ground Fault Circuit Interrupter's) https://www.icmag.com/ic/showthread.php?t=4315 Smoke Alarms…Detectors https://www.icmag.com/ic/showthread.php?t=16732 Fire Extinguisher: 101 https://www.icmag.com/ic/showthread.php?t=16728
__________________
>>>>>>>>>>>>>>>>>>>>>>>>>>>> > ICMAG OFFICIAL ~DIY~ LINK-O-RAMA https://www.icmag.com/ic/showthread.php?t=40637 A Library of Links https://www.icmag.com/ic/showthread.php?t=97792 How to replicate cannabis plants: ...various successful "cloning"/"cloner" techniques described w/ original posts linked https://www.icmag.com/ic/showthread.php?t=169382 A Complete Guide to Topping, Training and Pruning https://www.icmag.com/ic/showthread.php?t=115377 MEDICAL MARIJUANA SCIENTIFIC STUDIES REFERENCE GUIDE~2012~ https://www.letfreedomgrow.com/cmu/Gr...istJan2012.pdf Sharing Is Caring. IMB
Last edited by I.M. Boggled; 02-05-2012 at 10:40 PM.. |
|
|
1 members found this post helpful. |
|
|
#8 | |
|
PROFESSIONAL SURVIVOR
Join Date: Jun 2011
Location: In your head
Posts: 326
![]() ![]() ![]() |
Quote:
I have opted to just drop two 50 amp lines into the room instead of having to buy a sub panel on top of everything else. I assume this is going to be cheaper. I would just run a couple power receptacles off the lines and wall mount yes? And away we go? As far as that type of amperage draw goes, I have 3 1000 watt HID's, aeroflow 60 site with pump, portable AC/HEATER unit, 4 inline centrifugal fans, and other misc. pumps for the res. and cloner, as well as the chiller. I added it all up from the labels. I also just added another pump that draws 4.2 amps! lol It was attached to the bottom of a lobster tank. It retails for $350 but got it off Craigs List for $50. Boy does it blow some serious air ha ha. Any other suggestions? I'm all ears.
|
|
|
|
|
|
|
#9 | |
|
PROFESSIONAL SURVIVOR
Join Date: Jun 2011
Location: In your head
Posts: 326
![]() ![]() ![]() |
Quote:
So I assume that I can place 2 50 amp breakers in the new box, run the 6 Ga. wire into the grow room, but what do I attach to the end of these lines? How do I split them to be 120v per receptacle? I did call my power company and they said that it would be "okay" if I removed the tamper tag and pulled the meter to cut power off to my breaker box for replacement. Since I own the home and the area in which I live isn't known for electricity theft. That and the fact that she pulled my account and saw that I pay nothing lol. She told me to just make sure to call back the electric company to have them put a new tamper tag on. Thoughts?
|
|
|
|
|
|
|
#10 | |
|
Inveterate Tinkerer
![]() ![]() Join Date: Feb 2010
Posts: 6,090
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Quote:
Converting from 120 to 240 doesn't save you any money on the power bill. You are charged for wattage used, and that will remain the same. In order to carry the same amount of power on 120 as you can on 240, you will have to have much larger wire or twice as many circuits. 240v saves you money on the infrastructure, not the power bill. |
|
|
|
2 members found this post helpful. |
|
|
|
|