Be very careful you pay very, very, very close attention to what the superscript 1 next to #14, 12, and 10 stands for. It's real important. Electrical code is really nothing that one should learn via internet, although I understand where you are coming from with this. 310.16 is fine and good, but if one doesn't know the correct way to interpret it, including the impact of terminal device ratings, unguided and uneducated use could be a recipe for problems.
|
|
|
2 members found this post helpful. |
|
|
#3 | |
|
Guest
Posts: n/a
|
This is the most relevant part of that
Quote:
For most instances the insulation type will be THHN or THWN (suitable for wet locations) but Exception 1 supersedes what is written in 310.16. |
|
|
|
|
|
#4 |
|
Tired Farmer
![]() ![]() |
Any good info is worth posting. Its up to you to understand what it means.
__________________
#hammerheadgenetics |
|
|
|
|
|
#5 |
|
Member
Join Date: Jan 2013
Posts: 54
![]() |
310.16 really just tells you ampacity for wire gauge. However continuous loads over 3 hours in duration need to be multiplied by 1.25. Also voltage drop needs to accounted for. Then you check 250.66....
|
|
|
|
|
|
|
|