Register ICMag Forum Menu Features
You are viewing our:
in:
Forums > Marijuana Growing > Growroom Designs & Equipment > Grow Room Safety > Amp question for wiring new room

Thread Title Search
Click to buy Cannabis Seeds at Fast Buds
Post Reply
Amp question for wiring new room Thread Tools Search this Thread
Old 10-02-2011, 04:50 AM #1
michmedclones
Member

Join Date: Aug 2010
Posts: 159
michmedclones will become famous soon enoughmichmedclones will become famous soon enough
Amp question for wiring new room

Hey guys I have a quick question, I have an electrician coming over that I know and he needs to know the full load amps and voltage of my ballasts to get the right boxes and wires to run from my sub panel to my room. I want to run 4 1000w ballasts, I'm using these: https://www.hydrofarm.com/pb_detail.php?itemid=7627 Xtrasun 1000w mh/hps convertable ballast. I know I want to run 240v so I'm assuming that the voltage he needs, but I don't know the full load amps, I've read that the amp pull is 4.5 for a 1000w on 240v but I assume the fireup amp pull is higher and he wants to know that to make sure everything is kosher. If anyone can help me out I'd greatly appreciate it, I've tried to find it online and I'm having NO luck. One more quick question, for 4 1000w lights, fans, dehumidifier, enviromental controls, Co2 tanks, etc what size sub panel would you run? He was thinking 50-60 amps which sounds like more than enough but I don't want to have to change in the future. BTW its a 12x11 flower room.

Thanks guys
michmedclones is offline Quote


Old 10-02-2011, 05:26 AM #2
Electrician
Member

Electrician's Avatar

Join Date: Mar 2011
Location: California
Posts: 121
Electrician has a spectacular aura aboutElectrician has a spectacular aura aboutElectrician has a spectacular aura aboutElectrician has a spectacular aura about
I like to install 240Volt 1Phase 50amp subpanel in the room. It makes it very easy to add change/ loads in the future. Also 50amp MLO Load Center subpanels are cheap.
Electrician is offline Quote


Old 10-02-2011, 05:46 AM #3
michmedclones
Member

Join Date: Aug 2010
Posts: 159
michmedclones will become famous soon enoughmichmedclones will become famous soon enough
Awesome I thought 50 would be enough for 4 lights and accessories, thanks a lot.

If anyone knows about the amps I'd greatly appreciate it
michmedclones is offline Quote


Old 10-06-2011, 11:37 AM #4
RomulusUSA
Member

Join Date: Jan 2011
Posts: 420
RomulusUSA will become famous soon enoughRomulusUSA will become famous soon enough
Amp question for wiring new room

Figure 18a for the ballasts at 240v, and maybe 10a for everything else. I'd look at a 50a sub, and a 30a or 2x20a circuit for the lights. You could get away with two circuits of 14/3 honestly, well within capacity. Then another 15-20a (or 2) circuit for the accessories.

My veg/bloom room has a 50a breaker (wired for 95a, not nearly pushing it so have yet to swap breakers in either panel), 1x20amp@240, 1x15a@120 and 2x20a@120. Word of advice for the accessory circuits - do 4 or more duplexs! I did 2/ea and wish I had more in some locations.
__________________
"Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety." - Benjamin Franklin

Spring 2013 20 gallon AirPot grow
RomulusUSA is offline Quote


Old 11-02-2011, 11:26 AM #5
avant gardener
Banned

Join Date: Jun 2011
Location: punk rock gypsy.
Posts: 784
avant gardener is a glorious beacon of lightavant gardener is a glorious beacon of lightavant gardener is a glorious beacon of lightavant gardener is a glorious beacon of lightavant gardener is a glorious beacon of lightavant gardener is a glorious beacon of lightavant gardener is a glorious beacon of lightavant gardener is a glorious beacon of lightavant gardener is a glorious beacon of lightavant gardener is a glorious beacon of lightavant gardener is a glorious beacon of light
simple formula:
(watts/volts)x125%=amps.
this applies to single circuits as well as services and subpanels.

for instance, you want to run (4) 1000 watters on a singe 240v circuit, so:
4000/240=16.7 amps.

now add 25% to that figure to account for the extra load you'll draw when firing up:
16.7•1.25= 20.8 total amps.

you need at least a 30 amp circuit,
but long as you're pulling wire, i'd think about grabbing some 6 or 8 gauge wire and putting in more power in case you ever expand. it's much easier (read:cheaper) to do it now than to revisit it later.

figure the wattage on your other accessories and plug in the formula for as many circuits as you want to run. calculate the amperage (ermembering that most of these things are probably running on 120v), total them, round up, and you'll know how big a panel you need. again, i'd err on the side of a bigger sub just because you can. unless it's a long pull from the main service to your sub, the wire won't set you back too much either.
avant gardener is offline Quote


Old 11-02-2011, 12:11 PM #6
Gray Wolf
A Posse ad Esse. From Possibility to realization.


Gray Wolf's Avatar

Join Date: Apr 2009
Location: River City, USA
Posts: 9,402
Gray Wolf has a brilliant futureGray Wolf has a brilliant futureGray Wolf has a brilliant futureGray Wolf has a brilliant futureGray Wolf has a brilliant futureGray Wolf has a brilliant futureGray Wolf has a brilliant futureGray Wolf has a brilliant futureGray Wolf has a brilliant futureGray Wolf has a brilliant futureGray Wolf has a brilliant future
What AG said, but may I add?

A 1000 watt ballast isn't 100% efficient, so if possible look on the ballast name plate for actual amperage draw. The difference isn't huge, but it adds up.

Stagger your ballast and motor start ups, so as to not simultaneously spike your systems in rush amps.

Keep all of your ballast and motor loads, with high inrush current during startup, on separate circuits if at all possible. Look on the motors name plate for LRA (Locked Rotor Amps)amps.

Typically I design circuits at 80% load, to allow for voltage drop due to heat. What ever total amps I come up with, I just divide by 0.8.

In the case of 20.8 amps, 26 amps would be required to cover potential heat losses, so a 30 amp breaker would be adequate.

As already noted, what ever you think you will end up with is probably wrong, when you consider future possibilites, and the cost of wire and breakers is minimal to install a 50 amp sub panel.

Might I suggest that you also leave room for more breakers, for future brain farts?
__________________
An age is called Dark not because the light fails to shine, but because people refuse to see it.

Believing is seeing and ignorance is bliss until it bites you in the ass!

Fervor is the weapon of the impotent. The harder the sell, the poorer the product.

Alas, my ignorance abounds; the more I've learned, the less I know that I know..........

Thou shalt seek and respect the opinions of operators, even unto the third helper, for theirs is a wisdom unknown to technicrats.

Wise men learn more from fools, than fools from wise men.

In my dotage I finally discovered that the secret to putting on pants both legs at a time is sitting down.
Gray Wolf is offline Quote


Old 11-02-2011, 03:50 PM #7
growshopfrank
Senior Member

growshopfrank's Avatar

Join Date: May 2008
Location: evil store owner
Posts: 1,648
growshopfrank is just really nicegrowshopfrank is just really nicegrowshopfrank is just really nicegrowshopfrank is just really nicegrowshopfrank is just really nicegrowshopfrank is just really nicegrowshopfrank is just really nicegrowshopfrank is just really nicegrowshopfrank is just really nicegrowshopfrank is just really nicegrowshopfrank is just really nice
FWIW there is NO big inrush or spike with 1000w cap and coil ballasts period
growshopfrank is offline Quote


1 members found this post helpful.

Post Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT +2. The time now is 03:24 PM.


Click to Upgrade your account


This site is for educational and entertainment purposes only.
You must be of legal age to view ICmag and participate here.
All postings are the responsibility of their authors.
Powered by: vBulletin Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.