Old 03-31-2011, 10:44 PM #1
budshoteyes
Member

Join Date: Mar 2007
Posts: 381
budshoteyes will become famous soon enoughbudshoteyes will become famous soon enough
Stove plug to 50 amp sub panel?

Can a 50 amp stove plug be used to make a 50 amp panel for a grow room. The plug would be 2 ft long to the proposed panel....

Can it be done?
budshoteyes is offline Quote


Old 03-31-2011, 10:45 PM #2
krunchbubble
Dear Haters, I Have So Much More For You To Be Mad At, Just Be Patient....

krunchbubble's Avatar

Join Date: May 2008
Location: Bay Area,CA
Posts: 8,437
krunchbubble is a survivorkrunchbubble is a survivorkrunchbubble is a survivorkrunchbubble is a survivorkrunchbubble is a survivorkrunchbubble is a survivorkrunchbubble is a survivorkrunchbubble is a survivorkrunchbubble is a survivorkrunchbubble is a survivorkrunchbubble is a survivor
sure can....
__________________
3620 Watt Starlite LED Grow - Yield was 8 1/2 LBS!

https://www.icmag.com/ic/showthread.php?t=330640

1280 Watt Starlite LED Grow - Finished

https://www.icmag.com/ic/showthread.php?t=325694
krunchbubble is offline Quote


Old 03-31-2011, 10:58 PM #3
budshoteyes
Member

Join Date: Mar 2007
Posts: 381
budshoteyes will become famous soon enoughbudshoteyes will become famous soon enough
That was quick!

I just bought the plug 15 minutes ago,next step is panel and breakers and to learn all wiring considerations

I hope to be running 5 - 600 waters...only 3 lights will be on at any one time! + One fan and 8 air pumps

Thanks..... any wiring diagrams I can be pointed towards will be great!
budshoteyes is offline Quote


Old 03-31-2011, 11:05 PM #4
Electrician
Member

Electrician's Avatar

Join Date: Mar 2011
Location: California
Posts: 121
Electrician has a spectacular aura aboutElectrician has a spectacular aura aboutElectrician has a spectacular aura aboutElectrician has a spectacular aura about
Oh boy, another Oven Receptacle being used as a disconnecting means, with cord ends feeding a sub panel. This seems to be a trend around here. It can be done, not a recommended way, but to each his own, I guess.
Electrician is offline Quote


Old 03-31-2011, 11:09 PM #5
Electrician
Member

Electrician's Avatar

Join Date: Mar 2011
Location: California
Posts: 121
Electrician has a spectacular aura aboutElectrician has a spectacular aura aboutElectrician has a spectacular aura aboutElectrician has a spectacular aura about
If I was going to use that I would eliminate the oven outlet. Get some 6/4 SJO cord and use the oven outlet box as a junction box. Get a cord grip connector and a blank plate and splice your connections in that box that way it can't become unplugged. Run the SJO Cord to your desired panel location.
Electrician is offline Quote


Old 03-31-2011, 11:25 PM #6
budshoteyes
Member

Join Date: Mar 2007
Posts: 381
budshoteyes will become famous soon enoughbudshoteyes will become famous soon enough
My main reason for considering the plug to panel is that the main panel is 2 levels below the room and on the other end of the building. I would have to run 100 ft of line.

I spent 15 bux on the plug......to abandon the plug/oven To go a Safer route is definitely preferred!
budshoteyes is offline Quote


Old 04-01-2011, 08:56 AM #7
gardenbug
Member

Join Date: Apr 2010
Posts: 266
gardenbug will become famous soon enoughgardenbug will become famous soon enough
With that long of a run and that much power, make sure the wire in the stove plug is the appropriate size and in good condition. I would go with the hardwire suggestion, less plugs means less points of failure but it would work.
gardenbug is offline Quote


Old 04-26-2011, 04:30 PM #8
Catchin1
Banned

Join Date: Aug 2004
Posts: 131
Catchin1 will become famous soon enoughCatchin1 will become famous soon enough
what

what size is the wire in the box for the oven receptacle and how many are there. You know they could have run #8 up there and not #6 if they used copper. If there is just two conductors and a ground, then it would not be appropriate for a sub panel but if it has four wire in it two legs and a insulated neutral and an isolated bare ground then you will be fine to make it into a sub panel, provided that you separate and isolate your grounds and neutrals at this point.
You know "rigging" this stuff where you live and sleep is not cool. A electrical fire is not a good thing at all. The fiure dept comes in and starts bashing holes in walls, tracking mud and shit through the house and your insurance company when they find out it was due to something you "rigged" to make a grow op then they will not pay and you are screwed again.
Catchin1 is offline Quote


Old 04-26-2011, 05:50 PM #9
compost
Member

compost's Avatar

Join Date: Mar 2010
Posts: 608
compost will become famous soon enoughcompost will become famous soon enoughcompost will become famous soon enough
Quote:
Originally Posted by budshoteyes View Post
My main reason for considering the plug to panel is that the main panel is 2 levels below the room and on the other end of the building. I would have to run 100 ft of line.

I spent 15 bux on the plug......to abandon the plug/oven To go a Safer route is definitely preferred!
Electrician is not saying you have to run it from the main box. You can still use the oven line, only instead of running a plug from there to your panel just put in a juntion box. The reason being is that it is a much more STABLE connection and you can use the cord grip connector that he mentioned. Right off the 15 or take it back and spend less money on the parts needed to have it safe.
__________________
You ain't gonna learn what you don't wanna know.

So I give you my eyes and all of their lies,
Please help them to learn as well as to see.
Capture a glance, and make it a dance,
But looking at you is looking at me.
compost is offline Quote


Post Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT +2. The time now is 03:24 PM.


Click to Visit Sweet Seeds


This site is for educational and entertainment purposes only.
You must be of legal age to view ICmag and participate here.
All postings are the responsibility of their authors.
Powered by: vBulletin Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.