Post BASIC PRINCIPLES OF GOOD WIRING (fyi)

DANGER!:Please be wide awake and aware of the inherent dangers of electricity before starting to "play around" with it as it is mean and unforgiving and will viciously bite, perhaps even kill if not respected. IMB
>>>>>>>>>>>>>>>>>>>>>>>>>>>>>> >>>>>>>>>>>

Electricity can be an intimidating concept for many because of the potential danger.
You can virtually eliminate that danger with a little knowledge and proper safety practices.
However, regardless of how much knowledge you have, never become lax in dealing with an electrical system, or it can be deadly.



* Before beginning any electrical repair, shut off the power. Remove the fuse or trip the breaker for the circuit you will be working on in your service panel. Use a neon tester to be sure the power is off. If there is any doubt, you can remove the main fuse or trip the main breaker. Remember: Removing the main fuse or tripping the main breaker will usually shut off the power to the entire house.




* Electrical wires are color coded to prevent wiring errors.

* White wires almost always connect to other white wires or to chrome terminal screws on switches and receptacles.

* Some wiring devices–such as receptacles–are back-wired by pushing the bare wire end into spring grip holes. These wiring devices are plainly labeled to show which color goes into each spring grip hole.

* Switches are nearly always connected into black wires in cables. The only exception is where a cable is extended, making it necessary for the white wire to play the role of the black wire. When this is necessary, the white wires should be painted black to prevent future wiring errors.

* Study the wiring diagram.
This will help you understand the basic principles of good wiring.
Also, find a good electrical how-to book.
It's one book every homeowner should keep on hand for ready reference.

* Most home wiring is complete with either No. 14 gauge or No. 12 gauge wiring. No. 14 is the smallest wiring permitted under most codes.

* Always use the same size cable for a continuation of any extended wiring circuit.



CONNECT NEW WIRING TO LAST OUTLET IN CABLE

* New wiring should be connected to the last outlet in a run of cable. To locate the last outlet in the run, shut off the current. Remove the cover plates from each outlet on the circuit. The last outlet in the run has wires connected to only two of the four terminal screws.

* The two unused terminal screws on the last receptacle serve as a starting point for wiring to a new outlet.



ATTACHING CABLE FOR NEW WIRING

* Shut off the power to the circuit you will be working on at the service panel.

* Loosen the screws holding the receptacle in the box and remove it.

* Attach the white wire to the chrome terminal, the black wire to the brass terminal on the receptacle and to the box, if the box is metal.

* Use care to match the size of the original cable. If No. 12 wire is used, continue with No. 12. If No. 14 wire is used, use No. 14 for continuing the cable. The size of the cable is usually stamped on the side of the cable.

* New wiring can be connected to continue the run beyond the last receptacle . Note that the new wires are pulled through knockout plugs in the back of the outlet box.




ADDING NEW WIRING FROM A JUNCTION BOX

* New wiring can also be tied into a junction box, unless the wiring in the junction box is already at maximum capacity.

* Before tying in at a junction box, always trace the cables leading to the box to check the voltage. Be sure you are not connecting a 120-volt outlet to a run of wire providing 240 volts for larger appliances.

* To tie in new wiring at a junction box, first shut off the current at the service panel.

* Locate the main supply cable coming into the junction box from the service panel. Locate the supply wire by tracing the white wires. All white wires in the junction box will be attached to the white wire on the supply line

* Knock out the unused plug on the junction box and run the new line from the box as illustrated.
Be sure to use a cable clamp to secure the cable to the junction box.

TYING IN NEW WIRING AT A CEILING LIGHT

* You can tie in new wiring at a ceiling light if the light is not controlled by a switch.

* Shut off the current at the service panel.

* Tie white wires to white wires and black wires to black wires..

* Connect the ground wires as illustrated. If you are using a metal box, attach them to the box as well as the light fixture.

* Knock out an opening in the outlet box, and continue the new wiring as illustrated.
__________________

>>>>>>>>>>>>>>>>>>>>>>>>>>>> >
ICMAG OFFICIAL ~DIY~ LINK-O-RAMA
https://www.icmag.com/ic/showthread.php?t=40637
A Library of Links
https://www.icmag.com/ic/showthread.php?t=97792
How to replicate cannabis plants:
...various successful "cloning"/"cloner" techniques described w/ original posts linked

https://www.icmag.com/ic/showthread.php?t=169382
A Complete Guide to Topping, Training and Pruning
https://www.icmag.com/ic/showthread.php?t=115377

MEDICAL MARIJUANA SCIENTIFIC STUDIES REFERENCE GUIDE~2012~

https://www.letfreedomgrow.com/cmu/Gr...istJan2012.pdf
Sharing Is Caring.
IMB

Last edited by I.M. Boggled; 08-14-2010 at 06:49 PM..
I.M. Boggled is offline Quote


Old 10-26-2005, 08:41 AM #2
I.M. Boggled
Certified Bloomin' Idiot

I.M. Boggled's Avatar

Join Date: Jul 2004
Posts: 1,741
I.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really nice
Post ALWAYS MATCH CONNECTORS TO TYPE OF CABLE USED

* Some boxes come with built-in connectors.

* Armored cable connectors have inner rims to hold fiber bushings at the end of the cable.

* Nonmetallic cable connectors are designed to grip the installation around the cable with a two-screw clamp.

* Regardless of the type of cable used, always leave about 6" to 8" of wiring in the box to allow plenty of wire for making easy connections.

* You can tighten the nut on either type of cable connector by placing a screwdriver in the notch and tapping the screwdriver lightly.



MAKE ALL CONNECTIONS IN APPROVED BOXES

* Always remember that connections must be made in an approved box. Never connect one cable to another by an open-line splice.

* All switch, outlet, and junction boxes must be positioned so they are always accessible.

* You can easily remove knockout plugs with a nail punch, screwdriver or metal rod.



RUNNING NEW CABLE BETWEEN MULTIPLE FLOORS

* Drill a hole through the floor from bottom to top. Be sure the hole is drilled into the recessed area behind the wall rather than in the open. Be sure to use a bit that's large enough to permit free passage of the wiring cable.

* Run the cable through the newly drilled hole to the desired location for the new receptacle or switch .

* Bring the cable through the opening by using a weight on the end of a string and a wire with a hook on the end .

* Using this same technique, you can add one outlet to another by drilling up through the floor, pulling the cable under the floor, and then running it to the desired position on the opposite wall . The same wiring can be pulled through for either receptacles or switches.







ADDING NEW WIRING FROM BOXES IN CEILING

* If your home has an unfinished attic, it may be easier to add new wiring by attaching it to boxes in the ceiling. In this way, gravity works for you rather than against you.

* Attach the cable to the box as previously described.

* Cut a hole in the wall at the desired location for the switch or receptacle, and run the cable from the box in the ceiling to the new outlet location.

* Bring the new cable through the wall and ceiling by cutting and drilling holes in and through the wall, the 2x4 plate, and the ceiling. A special fish tape is available for these types of jobs.






ADDING NEW WIRING ON THE SAME WALL

* You can connect new cable from an existing outlet to a new outlet on the same wall by running it inside the wall. Mark the approximate location of the new outlet. Using a stud finder locate and mark the wall studs. Start one stud before the existing outlet and end one stud after the new outlet.

* Mark the exact location of the new box. Make it the same height as the existing box. Do not locate it over a stud. Using a drywall or keyhole saw, cut the opening for the new box.

* Using a utility knife and a drywall saw, cut a strip of drywall about 3" wide out of the wall, below the outlets. Start at the center of the first stud you marked and end at the center of the last stud; watch for nails as you cut. Carefully remove the drywall strip.

* Using a hand or circular saw, make two cuts 1" apart and 3/4" deep in each of the exposed studs. Using a hammer and a chisel, remove the wood between the two saw cuts.

* Be sure the power is off to the existing outlet.
Remove the cover plate and the receptacle. Remove one of the knockouts in the bottom of the box. Run the new wire behind the wall and up through the knockout in the box. Tighten the clamp and attach the wires. If the box does not have a clamp, place a wire clamp on the new cable. Tighten the screw to hold the clamp on the wire. Be sure the nut is off the wire clamp and run the wire up to the box as before. Feed the threaded end of the clamp up through the knockout, replace the nut and tighten. Replace the receptacle and the cover plate.

* On the new box, remove one of the knockouts in the bottom of the box. If the box you are using is a self-clamping box, insert the box into the wall and tighten. If not, insert the box into the wall, insert a Madison hanger on each side of the box, and bend the tabs over into the box to tighten.

* Finish running the wire from the existing box through the notches and up behind the wall into the box as before. Clamp the wire and install the receptacle as in Fig. 3. Install the cover plate, turn on the power, and test the circuit with a neon tester. Shut off the power again to safely finish the project.

* Nail metal cable protectors to the exposed studs over the notches. Replace the drywall strip you removed earlier. Use the spackling compound and drywall tape to complete the installation.

* Cable can be pulled from an existing box on one wall to a new outlet on the opposite side of the same wall.

* Attach a cable to the existing receptacle in the box as previously described. Allow ample slack in the cable to permit easy connection to the new box to be installed on the opposite wall.

* Bring the cable through the new opening with a wire.

* Connect the cable to the new box, attach the desired receptacle, and mount the box to the wall with box supports if it is not near a stud.

https://doityourself.com/electric/index.shtml
__________________

>>>>>>>>>>>>>>>>>>>>>>>>>>>> >
ICMAG OFFICIAL ~DIY~ LINK-O-RAMA
https://www.icmag.com/ic/showthread.php?t=40637
A Library of Links
https://www.icmag.com/ic/showthread.php?t=97792
How to replicate cannabis plants:
...various successful "cloning"/"cloner" techniques described w/ original posts linked

https://www.icmag.com/ic/showthread.php?t=169382
A Complete Guide to Topping, Training and Pruning
https://www.icmag.com/ic/showthread.php?t=115377

MEDICAL MARIJUANA SCIENTIFIC STUDIES REFERENCE GUIDE~2012~

https://www.letfreedomgrow.com/cmu/Gr...istJan2012.pdf
Sharing Is Caring.
IMB

Last edited by I.M. Boggled; 10-26-2005 at 08:54 AM..
I.M. Boggled is offline Quote


Old 10-26-2005, 09:03 AM #3
I.M. Boggled
Certified Bloomin' Idiot

I.M. Boggled's Avatar

Join Date: Jul 2004
Posts: 1,741
I.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really niceI.M. Boggled is just really nice
Post

Ground-Fault Circuit Interrupters

A Ground Fault Circuit Interrupter (GFCI) detects any loss (leakage) of electrical current in a circuit that might be flowing through a person using an electrical product.
When such a loss is detected, the GFCI turns electricity off before severe injuries or electrocution can occur. (However, you may receive a painful shock during the time that it takes for the GFCI to cut off the electricity.)

GFCI wall outlets can be installed in place of standard outlets to protect against electrocution for just that outlet, or a series of outlets in the same branch.

A GFCI Circuit Breaker can be installed on some circuit breaker electrical panels to protect against electrocution, excessive leakage current and overcurrent for an entire branch circuit.

Plug-in GFCIs can be plugged into wall outlets where appliances will be used.


Electrocution prevention w/ GFCI's
https://www.icmag.com/ic/showthread.php?t=4315

Electrical Safety For Indoor Growrooms
https://www.icmag.com/ic/showthread.php?t=15468

__________________

>>>>>>>>>>>>>>>>>>>>>>>>>>>> >
ICMAG OFFICIAL ~DIY~ LINK-O-RAMA
https://www.icmag.com/ic/showthread.php?t=40637
A Library of Links
https://www.icmag.com/ic/showthread.php?t=97792
How to replicate cannabis plants:
...various successful "cloning"/"cloner" techniques described w/ original posts linked

https://www.icmag.com/ic/showthread.php?t=169382
A Complete Guide to Topping, Training and Pruning
https://www.icmag.com/ic/showthread.php?t=115377

MEDICAL MARIJUANA SCIENTIFIC STUDIES REFERENCE GUIDE~2012~

https://www.letfreedomgrow.com/cmu/Gr...istJan2012.pdf
Sharing Is Caring.
IMB

Last edited by I.M. Boggled; 10-10-2006 at 09:51 AM..
I.M. Boggled is offline Quote


Old 10-26-2005, 09:53 AM #4
Guest
Guest

Posts: n/a
Good Info IMBoggled.
Wiring is intimidating but VERY easy to learn it you respect it.

It should be doubly stressed that all connections HAVE TO BE MADE INSIDE ELECTRICAL BOXES! !

No wire nuts a dangling
Quote


Old 10-26-2005, 10:49 AM #5
Loblolly1
New Member

Loblolly1's Avatar

Join Date: Oct 2005
Posts: 22
Loblolly1 is on a distinguished road
Great information, much thanks.
Loblolly1 is offline Quote


Old 10-26-2005, 10:59 AM #6
Guest
Guest

Posts: n/a
indeed, thanks for all of the great pictures. visual refferance can be very reassuring when it comes to electrical.

-ms
Quote


Old 10-26-2005, 01:32 PM #7
guineapig
Moderator


guineapig's Avatar

Join Date: Aug 2005
Location: In spite of my rage I am still just a rodent in a cage
Posts: 4,610
guineapig has much to be proud ofguineapig has much to be proud ofguineapig has much to be proud ofguineapig has much to be proud ofguineapig has much to be proud ofguineapig has much to be proud ofguineapig has much to be proud ofguineapig has much to be proud ofguineapig has much to be proud ofguineapig has much to be proud ofguineapig has much to be proud of
on a related note once, when i was young and foolish, i bought an ionizer and put it in a small closet which was lined with mylar.....everything was fine until the mylar developed wrinkles and i was suprised when little blue sparks began to jump around the creases in the mylar! so i suppose remember- if you are working with mylar it can still conduct electricity albeit a very small amount. just remembered that story! -gp
guineapig is offline Quote


Old 02-05-2006, 09:35 AM #8
Guest
Guest

Posts: n/a
Here is a quick guide below for residential wiring sizes and breakers in the United States most growers are likely to encounter.

Dudes are sometimes wondering what size wire should go with what size breaker. Don't ever skimp in this area as this is probably the biggest reason fires occur for growers.

* Note: When working with electrical wiring, bigger is always better as a rule of thumb for wire sizing. If you are exceeding ~ 100 feet in length in electrical run, make sure you "upsize" your wiring one size to compensate for line loss due to the length of wiring.

Here is a quick chart for COPPER WIRE ONLY:

14 AWG = 15 Amp Breaker
12 AWG = 20 Amp Breaker
10 AWG = 30 Amp breaker
8 AWG = 40 Amp breaker

* Note: Do not exceed 80% of a breakers capacity for safety. For instance, a 20 amp breaker should have no more than 16 amps on that circuit. (80% x 20 amps = 16 amps.

*15 amp breaker x 80% = 12 amp max load.

Add up all the amps of all your appliances on any given circuit to make sure you are indeed "safe" and stay at 80% or under of the breakers capacity.

Last edited by ThunderBolts; 02-05-2006 at 09:36 AM..
Quote


Old 02-05-2006, 12:02 PM #9
UV Dreams
Member

UV Dreams's Avatar

Join Date: Oct 2005
Location: Earth
Posts: 47
UV Dreams is on a distinguished road
Quote:
Originally Posted by ThunderBolts
Here is a quick chart for COPPER WIRE ONLY:

14 AWG = 15 Amp Breaker
12 AWG = 20 Amp Breaker
10 AWG = 30 Amp breaker
8 AWG = 40 Amp breaker

* Note: Do not exceed 80% of a breakers capacity for safety. For instance, a 20 amp breaker should have no more than 16 amps on that circuit. (80% x 20 amps = 16 amps.

*15 amp breaker x 80% = 12 amp max load.

Add up all the amps of all your appliances on any given circuit to make sure you are indeed "safe" and stay at 80% or under of the breakers capacity.

Here is the above example for safe amperage limits broken down into watts that most of us are familiar with.

15 AMP x 120V = 1800 watts @ 80% = 1440 watts
20 AMP x 120V = 2400 watts @ 80% = 1920 watts
25 AMP x 120V = 3000 watts @ 80% = 2400 watts
30 AMP x 120V = 3600 watts @ 80% = 2880 watts

30 amps should be high enough for this chart. If you are running any more than 30, you should know what you are doing.
UV Dreams is offline Quote


Old 02-05-2006, 08:01 PM #10
Guest
Guest

Posts: n/a
Another major "no-no" is double tapping or double lugging a circuit.

Instead of adding another breaker, some people will tap a new circuit onto an existing occupied breaker. This is a no-no. This is identified by MORE than ONE wire coming off a breakers lug (the part where the wire is attached).

Another "no-no" is undersized wiring. I have seen 14 awg tapped into 30 amp breakers (too small wire size) and your wire will melt and catch fire before the breaker trips. Ouch !!! Skinny ass extension cords are fires waiting to happen.

If in doubt, get a licensed electrician because your life and home are at stake.
Quote


Post Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT +2. The time now is 11:56 AM.




This site is for educational and entertainment purposes only.
You must be of legal age to view ICmag and participate here.
All postings are the responsibility of their authors.
Powered by: vBulletin Copyright ©2000 - 2019, Jelsoft Enterprises Ltd.