#41
|
||||||||||
|
||||||||||
|
Quote:
Any time you have neutral and grounds terminated to the same busbar, the panel in question has to be fed with SEU, or in other words, the neutral doubles up as a grounding conductor as well. Inaccurate statement but will have to do I guess. The job of a neutral conductor is to carry the return current back to the source, as I've stated, but it's important to know that the neutral carries the imbalance of the load. Say, in my main panel fed with SEU, One incoming hot leg (or phase) is drawing 60 amp. The other hot leg is drawing 40amp. This current draw is being utilized by your branch circuits feeding your entire house. The return current traveling back to the transformer is not 100 amp. It's 20 amp. This is why neutrals are allowed to be smaller than the hots in some instances. This is why it's good to balance the loads in your panel also. If you know 2 appliances are likely to be running at the same time, then put them on opposite legs. On the other hand, you would put a separate AC unit and furnace on the same leg because you know they'll never be running at the same time. Kitchens are required to have 2 - 20A small appliance branch circuits. I generally stab them onto different legs. The same holds true when using Multi Wire Branch Circuits (Using a 14/3 to feed two separate 120v loads but sharing the neutral). If both 120v loads are drawing 10A, then the return current on the shared neutral will be 0. So anyway, the grounded conductor (neutral) of your SEU Main Service Cable should never see a "full" load. EDIT: The arrangement of the hot bus bars is naturally set up to stagger but you can unbalance your panel easily if you don't think about what goes where before hand. Say you run a sub-panel for your grow room and you choose to start attaching breakers down the left side of the panel. This is the arrangement you happen to put the breakers in (on the left hand side only) 20A Single pole - 1000w dedicated ballast for bloom - Phase A (L1) or "leg" as I call them 15A Single pole - Ceiling light fixture to throw a green CFL into - Phase B (L2) 20A Single pole - 1000w dedicated ballast for bloom - Phase A 15A Single pole - dedicated water and air pumps for reservoir. - Phase B 15A Single pole - dedicated 600w for grow - Phase A You've got a seriously imbalanced panel there. As long as you sized the feeder cable appropriately, there still not really an issue but it's bad planning to arrange breakers like that. You should have done: 20A Single pole - 1000w dedicated ballast for bloom - Phase A 20A Single pole - 1000w dedicated ballast for bloom - Phase B 15A Single pole - Ceiling light fixture to throw a green CFL into - Phase A 15A Single pole - dedicated water and air pumps for reservoir. - Phase B 15A Single pole - dedicated 600w for grow - Phase A Study the empty hot busbars on a de-energized panel and you'll see how they are staggered.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit Last edited by madpenguin; 04-21-2009 at 12:01 PM.. Reason: Added "Phase A" and "Phase B" for clarification |
||||||||||
|
#42
|
||||||||||
|
||||||||||
|
Quote:
Don't get mad, just pulling your chain. That's why I use Galaxy ballasts with sunlight reflectors..... As an added bonus, you can use Galaxy on 120 or 240... So... I guess my original statement holds. With proper planning, it really shouldn't be an issue. I know things go bad sometimes after the warranty has expired. Sure. Fix it yourself, if not send it back if it's still under warranty. I know it's not the most economical approach, but I keep backups of all my equipment. 396gph ecoplus pump goes out? No problem. Got another one in the basement. Same with a spare 600w ballast. While I'm waiting on my RMA, I just use the new one. But yes, you have a valid point, most certainly. Many situations arise whn you need to do the work yourself. In that case, just make sure you know what your doing 100% before you start.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
||||||||||
|
#43
|
|||||||||
|
|||||||||
|
Great information... keep it going!!!
BTW - Pigtailing does make a lot of sense so you don't lose downstream equipment if an upstream outlet goes bad, etc... Most everything in a room for me is typically on it's own circuit except for my two green light receptacles. I like the sharing of resources and the civil way people are discussing topics and code. Thanks guys!
__________________
“A question that sometimes drives me hazy: am I or are the others crazy?” - Albert Einstein
|
|||||||||
|
#44
|
|||||||||
|
|||||||||
|
madpenguin..Sorry left yesterday after my last post..I'll concede you are probably right and a single circuit probably is allowed to be spliced at the yoke..
I mostly work on 120/208v..277/480v 3Ph systems..and do a lot of office buildings..we pigtail everything.. more for the reason Phillthy just stated.. When a receptacle gets used alot..plug-in/plug-out like a vacuum location..I've seen this as a failure point.. especially when using the stab-in connections..and the mounting isn't solid to the wall(spongy) I've had two service calls in homes where the problem was open neutral at a yoke and also took out devices downstream.. If it had been pigtailed..then the failure will most likely stay at that one device..Klein twisted solid wire, then nutted connections rarely fail if done right.. Sub-panels and N & G..At some point at the service entrance(step-down transformer, main panel, main disconnect) at or before the 1st means of disconnect..we bond Neutral & Ground together..(Neutral is also known as the Grounded conductor..and Ground is known as Grounding conductor) Since in residential this is usually done at the main panel..you may see a green screw bonding the N bus to the enclosure..(this screw or wire is called the Main Bonding Jumper) After this bond is made..all downstream devices or Sub-panels need to isolate the ground and neutral from each other.. So if your new sub-panel comes with a bonding screw you won't use it.. The reason is if there is a fault (hot to ground) on the load side of your sub-panel, it will only travel on the green grounding conductor all the way back to the main bonding point..which is also tied to Earth Ground If it were bonded again at the Sub..the fault current could travel down the neutral feeder from the sub to the main..or normal return currents from the neutral could travel down the Green to the main.. If all is wired right..no current should be on the green in a non-fault situation.. Since they are usually(not always) bonded at the main panel in residential..some guys don't install an Equipment Ground Bus at the main and just use unused neutral lugs.. not acceptable at sub-panels fed from the main..
__________________
" Want some whiskey in your water, Sugar in your tea...What's all these crazy questions you asking me...This is the craziest party that could ever be..Don't turn on the lights cause I don't want to see..Open up the window, Let some air into this room..Think I'm almost choking from the smell of stale perfume..And that cigarette your smoking bout scare me half to death..Open up the window sucker, let me catch my breath.."I'm Governor packn2puff and I approve this message Newest!! BubbleDust Picfest |
|||||||||
|
#45
|
|||||||||
|
|||||||||
|
FWIW - These posts are GREAT.
Respect to those adding to the discussion!! Just an FYI for those trying to do more research ... those GREAT pictures that madpenguin has been nice enough to share ... can be found in the excellent electrical resource : Black and Decker's Complete Guide To Wiring ... https://www.amazon.com/Black-Decker-C...9730408&sr=8-1 Hope it Helps SYK |
|||||||||
|
#46
|
|||||||||
|
|||||||||
|
It is my understanding that the new code states that sub panes for out buildings and such are now required to travel back to the main for earth ground. It is no longer appropriate to have a separate earth ground for a sub panel. Anyone have more info on this?
__________________
“A question that sometimes drives me hazy: am I or are the others crazy?” - Albert Einstein
|
|||||||||
|
#47
|
|||||||||
|
|||||||||
|
I recently heard of a code inspection for 2 - 200A Subs that *some guy* put in *his* garage.
The subs were bonded together (technically this was done using the unistrut which it was mounted on) - but for the inspector *this person* added a shielded #6 between the panels. The Grounding Bus was then taken to a grounding rod (also using #6), buried 8 feet deep. In Addition - *they* ran a #4 back from the panels to the main SE (250') where it was connected to *their* new 400A main panel and dual grounding rods. Inspector said it was overkill and *his* install/work was akin to jobs that he had seen done for Hospitals and Schools. Not sure if that helps? SYK |
|||||||||
|
#48
|
||||||||||
|
||||||||||
|
Quote:
You also need a ground rod (grounding electrode) driven at the detached structure regardless. This includes rinky-dink sheds. If the structure is not physically attached (wall to wall) with the house, then it's considered detached. So, an 8' steel rod that is copper plated needs to be driven. If you measure 25 ohms of resistance or more, then you need to drive another rod. Ground rods are cheap, I usually drive 2 just so it's a non issue. It's also very hard and time consuming to accurately measure resistance on a grounding electrode. When driving 2 rods, the first one must be outside the drip edge of the roof. You want it in contact with moist earth. Then the second one needs to be atleast 6 feet away from the first. I do it at 8 feet. Clamps used to connect the ground rods to the isolated ground bus in the sub need to be rated for direct burial. You would use #6 bare copper to connect the ground rod/s to your isolated grounding busbar. This is all in conjunction with your dedicated grounding conductor leading back to the house (part of the feeder cable). Also pretty sure any exposed GEC/EGC (Grounding Electrode Conductor - #6 bare wire) needs to be protected from physical damage on the outside of the structure. Don't think shedule 40 will do it, has to be schedule 80 PVC or RMC/IMC. Rigid Metal Conduit or Intermediate Metal Conduit. Inspectors usually overlook this but some can be pricks about it. I challenge anyone to severe a #6 with a weed eater. A lawn mower will do it tho so make sure it's adequately buried and plumb/flush with the structure if your not using conduit to protect it. Any detached structure being fed from the house also needs a main disconnect, on the outside of the structure, or immediately inside the structure. What I usually do is buy a Main Breaker Panel (not a MLO) and as soon as the feeder cable enters the building, it goes directly into the panel. Basically the same principle as your main panel in the house (even tho the feeder cable is now fused by the main panel at the house). Even if your not installing a sub-panel, you need a disconnect imediately inside the detached structure. Say I just wanted to run 2 lights and have one receptacle in my shed. I could use 14/2 UF romex coming out of my main panel and just direct bury the cable. But as soon as it entered my shed, I would need to run it into a junction box with a single pole light switch. All power to the shed needs to be killed when I throw that switch. There is also burial depth requirements for cable and conduit. Table 300.5 So, If I wanted to protect that 14/2 direct burial UF cable with a GFCI breaker in the main panel, then I would only have to bury it 12". You also wouldn't need a grounding electrode in this instance. Only when your feeding a sub-panel. If the framing of the detached structure is exposed, then you need to run all your wire in conduit. Not romex but individual THHN conductors. Or, you could sleeve all romex with EMT or Electrical PVC conduit. Up to a height of 8 feet I believe.... If the structure has metal framing, then you need to ground the framing to your isolated ground busbar as well. Ugh... Lots of stuff but that's it in a nut shell. Just use common sense and protect your wire and you will automatically comply with much of the NEC.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
||||||||||
|
#49
|
|||||||||
|
|||||||||
|
Excellent information. Thank you for sharing!!!
__________________
“A question that sometimes drives me hazy: am I or are the others crazy?” - Albert Einstein
|
|||||||||
|
#50
|
|||||||||
|
|||||||||
|
I added more pics on page 2 of this thread. The post concerning a sub panel installation..
I'll go ahead and wrap up and post branch circuit runs and installing breakers in the sub panel for those of you who are interested. Pretty simple but some of you probably have never done it so I'm going to be very basic. Set your junction boxes first. Don't worry about putting cable into them, just set them (so ignore the cable inside the box below). If this is a new room with exposed framing, all the easier. A typical rule of thumb for receptacle boxes is hammer height to the bottom of the box. If your studs are exposed, then new work boxes are what you want. They have the nails in them that attach to the side of the 2x4. This is a double gang new work box. Will accept 2 devices. See those 2 little peg things that are in front of the 2x4? Blue and part of the box? The ends should butt up against the front of the 2x4. Using those as guides to set the box, when you go to hang drywall, the front of the outlet box will be flush with the drywall. Grab your roll of cable and start at the set junction box and work your way to the panel. Don't try to fish the cable thru the knockout in the back of the box, just start in the stud cavity that your box is in. ![]() When unreeling romex from the roll, Take the outer loose end and step on it so it's flat. Then start walking with the roll and unraveling it and keep stepping on the romex as you go. Hope that makes sense. Don't just grab the cable and pull it off the roll while it is laying on the floor. You'll have a kinked and twisted mess. Your cable should be nice and straight with no kinks. Once you "walk off" 20 feet or so, put the roll down and run your cable. Rinse and repeat until you get to where you need to be (the panel). Once you reach the panel, leave the cable attached to the spool still. It should still be sitting back at your outlet box. Approximate how much cable you'll need to take into the panel. Always try to take your cable into the top of the panel. Looks really shitty when you use the sides and bottom. You need a proper pair of wire strippers: Notice towards the tip, there is a place for 14/2 cable and then 12/2 cable. That's how you strip the outer sheathing off of romex. Not like this: That's the sign of a hack. If you don't own wire strippers then you have no business doing electrical work in the first place.:wink: Don't write all over your cable like that either. Looks like an 8 year old did it. Don't twist all your ground wires together like that either. This panel is absolutely horrid. Notice how he over stappled everything in the pic below as well. Possible bending radius violation along with unsightly side entrance cable and 8 year old writing... (ignore the arrow) You'll need to remove a knock-out from the top of the panel. Use a flathead screw driver and your lineman's pliers to break it loose. Then install a NM connector with the screws on the outside of the panel. Never put more than 2 cables in one 3/8" NM connector. 2 - 14/2's or 2 - 12/2's. Only one 10/2. One 14/3, one 12/3 and one 10/3.... Pretty much common sense. Here is a crappy plastic one. Much prefer the metal ones. Once you have your NM connector installed and tightened down really good, pull your 14/2 cable into the new sub-panel. Pull enough in so all conductors in the cable will reach their intended destination. It should still be attached to the roll at this point if you started working from the outlet box. When you have enough, take a black sharpie and mark the cable where you want to strip it as it enters the panel. Remember to leave 3/8" of the outer sheathing inside the panel and remove the rest. Once you crimp it with your wire strippers where you marked it, the entire sheathing will pull right off the conductors. Helps to wiggle your strippers from side to side so it cuts all the way through the sheathing (but it will not damage the individual conductor insulation). Remove the paper wrapping that surrounds the ground wire as well. Once your branch circuit cable is in place, stripped and the nm connector has been snugged down onto the cable (do not over tighten the screws), work backwards towards the outlet box. Start stapling your cable down and pulling any excess with you back towards the outlet box. You might want to hold off stapling until all your cable is run. You can fit 2 - 14/2's or 2 - 12/2's under one staple. If you staple each branch circuit as you go, you might find yourself pulling staples down the road to accommodate for new branch circuits.... Your cable must be atleast 1 1/4" inch from the face of the framing member. This is to prevent drywall screws from hitting your cable. So, always staple dead center of the 2x4. Same deal when you drill through a 2x4 to run horizontally. Put the hole dead center, otherwise, a drywall screw could pierce your cable. No need to use anything larger than a 3/4" auger bit when drilling. You should also only have 3 cables in one hole. If you need to drill more than one hole, put twice the width of your auger in between holes. So, if using a 3/4" auger bit and you need to drill 2 holes, from inside edge to inside edge of the holes, give yourself 1 1/2" of space. When driving staples, just make sure the cable is snug to the 2x4. Don't over do it. If you take a pair of dykes (side cutters) and pull the staple up and you see a noticeable indentation in the outer sheathing, then your probably driving your staples too much. Cables should be stapled to within 12" of an outlet box and every 4 feet there after (I like to do it 6" and 3' respectively). Watch your bending radius with the cable. No sharp 90 degree angles. Same reason we don't want kinks taking it off the spool. Your likely to get increased resistance at those points. Once you make it back to your outlet box, measure how much wire you will need to have atleast 6-8" sticking out the front of the box, then cut it off the roll. You can always cook a rare steak more but once it's over cooked your screwed. My point being, always leave extra. If you cut the cable too short, you need to pull the entire run and start over. Don't even think of making splices outside of an approved junction box. That's their main purpose. To contain fire if it starts. Also, don't even think of installing a junction box to splice wires and then cover it up with drywall. All junction boxes need to be accessible at all times. If you cut your wire too short and don't want to re-do the entire run, then you must install another outlet box just as you did for the receptacle location. Then once your drywall is up, you would put a blank plate on the junction box so you can still get at the wires later. When you insert the wire into your box, do not break the tab off. For that matter, don't even bend it down too much. Just jab at it with a screw driver to break the initial "lock" it has, and then carefully fish the end of your cable into the box. You want the plastic tab to retain it's "springyness" and to firmly hold the cable in place. Always leave 3/8" inch of outer sheathing in your outlet box as well as your panel. I forget what the NEC says. Pretty sure it's 3/8". From the point where the cable enters the outlet box, you need at least 6" of conductors. That will typically leave you with at least 3" sticking out of the box. Make sure you do this! Old timers back in the day would leave 0" sticking out of the box. How they even managed to device anything out is beyond me. I hate working with short conductors. Really pisses me off and it will you too... Here's what I do. Your strippers should be 8" long. Crimp the outer sheath as shown above where you need it. Put the tip of your strippers at the cut point of the sheathing you just made. Mark where the cable meets the end of the handles. Cut there. That leaves you 2" extra beyond what code requires. Once the wire is ran, cut and stapled, go back to the panel. You should have 3 loose conductors from the branch circuit you just ran. Remember the order in which to hook things up (ground, neutral, hot) and reverse to unhook (Hot, neutral, ground). Terminate the grounding conductor: No more than 2 grounding conductors under one screw. Terminate the grounded conductor: One conductor per screw. No more. Then attach the ungrounded conductor to your breaker: Put the hooked end in first: Then push it into place so it makes contact with the hot busbar: Your done in the panel. Go back to your outlet. The cable is already cut, stripped, stapled, 3/8" of sheathing enters the box and at least 3" of conductors are sticking out the front. Making up receptacles is very easy. Just remember "Black to Brass will save your ass". Black to brass, Ground to green and white to silver. Again, remember your connection order (even tho every thing is cold). Just get into the habit of it. Also, again, never backstab a receptacle. They are the little holes in the back: Use the screw terminals. If it's a spec grade receptacle (heavy duty), there will be slots right by the screw terminals. Use them. If it's a spec grade receptacle (or 20 amp receptacle), you don't need to put little loops in the end of your conductors to attach. Just leave them straight, strip the ends and insert into the slot and tighten down the screw. Tighten them down good. You can usually do better with a flathead than with a phillips. Stripping the ends of your conductors: If it's not spec grade and just your standard 49 cent receptacle, put little bends at the ends of your conductors. There is a little hole on your wire strippers that is made for this. Look at the above pic. Inbetween his thumb and the neutral wire, right below the word "only". Stick the end of your stripped conductor in that hole. Just have a hair of wire sticking out the other end and then use your wrist and do a 180 degree bend (with the stripper hand, not with the conductor hand). The wire will wrap around the edge of the strippers to form a hook. As someone already mentioned, hook the conductor onto the terminal screw so that when you tighten down the screw, it grabs the wire and pulls it tight. If you do it the other way, it will start to squeeze the wire out. Always push the bare grounding conductor into the back of the box first. Treat it the same way as you make connections. Push the excess ground in first, then neutral, then hot. You don't want that bare grounding conductor to accidentally make contact with a hot or neutral screw terminal. Anyway... That's branch circuits 101.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit Last edited by madpenguin; 04-15-2009 at 10:40 PM.. Reason: Added more detailed info |
|||||||||
|
|