#31
|
|||||||||
|
|||||||||
|
Awesome information here! To all who've shared, this is a tremendous resource. Many thanks!
__________________
The fates lead him who will; him who won't they drag. - Seneca |
|||||||||
|
#32
|
|||||||||
|
|||||||||
|
You basically want to create a low impedance dedicated return path for any ground fault current if it occurs. The neutral wire of the feeder going back to the main panel should only carry the return current at all times, just as a 14/2 branch circuit neutral should only carry the return current at all times.
There should only be one point where neutral and ground are bonded together and that's typically in your main panel, or rather, at your main service disconnect (which can sometimes be outside in a separate enclosure). On a semi related note, in most houses you have the meter outside and the main panel in the basement practically 5 feet away from the meter. The incoming SEU cable is unfused so it has to go directly into your main panel with the service disconnect, otherwise it's a potential fire hazard. If the SEU cable had to travel more than 5 feet or so inside your house, you need to have your main service disconnect outside, and then use SER from the disconnect to your "main panel". Then you would need to attach the ground rod and water meter bond to the outside disconnect instead of your panel (they would attach to the neutral in the outside disconnect). There are many different requirements if your installing a sub-panel in a detached structure (garage, shed, barn). The above post was for a sub-panel in the same house as the main panel.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
|||||||||
|
#33
|
||||||||||
|
||||||||||
|
Quote:
Also why you don't want to terminate any neutral wires to the dedicated ground basbar in a sub-panel. You would have objectionable current on the frame of the panel. If you didn't use the bonding bar/strap/screw, then you force the neutral current to travel down the grounding conductor. If you did use the bonding bar/strap/screw, then your back to having parallel paths, along with objectionable current on the frame of the panel.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
||||||||||
|
#34
|
|||||||||
|
|||||||||
|
Just know that current always wants to get back to it's source, which is the center tap at the transformer. It doesn't care how it gets there, just that it does.
I was working at someones house and the bonding jumper to the water meter shocked the shit out me. It read constant voltage. Threw her main disconnect and it still read voltage. ![]() That's when I call the Power Company. It turned out that the next door neighbor had a loose neutral at their disconnect. All the current they were using had no where to go (back to the transformer on the pole), so it traveled down their bonding jumper to their water meter, out thru their front lawn on the water pipe, down the street about 20 feet, and back up thru this lady's house to her water meter, across her bonding jumper and then out her neutral to the transformer. This is why you absolutely do not switch neutrals. You'll still find switched and fused neutrals in old houses with Knob & Tube wiring. So.... It always want's to go back to the source and doesn't care what path it takes (including you). When you wire, you need to force it to take the most safest route and least resistive route.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
|||||||||
|
#35
|
||||||||||
|
||||||||||
|
Quote:
ACtually it IS the more complicated stuff that we cant outsource. I used Sunsystem ballasts with Hydrofarm hoods. Who am I going to call to cut the plugs off and hardwire them? Nobody, I had to do it myself. If a ballast goes bad, who am I going to have fix it? Nobody, myself. And if setting up a 5000+ grow, you cant really have an electrician in. There is no reasonable reson for wanting so much power, in such a small space with outlets everywhere you need it. It would be nice if we had a dedicated electrical section where anyone could post topics, but only a qualified few could respond. The info posted here is very helpful |
||||||||||
|
#36
|
||||||||||
|
||||||||||
|
Quote:
I have been shocked with 110 I have seen a friend after he was zapped with 277 glad it wasn't 480.electricity is something definitely to be anal about if you want to live long.just like you shouldn't disable or put awater heater without a t.m.p. valve. I have taking a lot of code related subjects ,plumbing,concrete,building,fo r all of you old far electricians hands hurting frrom fucking with wire.you need,no should get your inspection certification,and anything else you can cert yourself.concrete,pulmbing,bui lding code,mechanical,hvac. thelatest one coming down the pipe is A.D.A. all new buildings will in the future require an inspection certification for compliance with all provisions of this act as it relate to buildings. lastly I figure if someone wants to fuck with electricty without seeking consultation checking,backchecking or waiting to hear from you certified guys if its right wrong.then they are a canidate for a darwin award. and don't feel to bad people die all the time,and the world has enough so feel good if you contribute to population control. ![]()
|
||||||||||
|
#37
|
|||||||||
|
|||||||||
|
Just to let you all know..this is now considered a code violation by the NEC.. Neutral connections need to be pigtail spliced these days(like the green ground is shown)..not made at the yoke of the receptacle or device.. Was a common practice back-in-the-day.. Sorry didn't read the whole thread..but I'll also share that ampacity is related to wire insulation..the chart provided is for 90C rated wire like THHN.. Fortunately most insulation these days is THHN..for other insulation types and ambient temps it's used in see National Electrical Code table 310.16 "But packn I don't have a code book"..well my friends there is a very helpful little book at Hemp Depot..ahhh Home Depot..in the electrical dept.. called the Ugly's book..has common charts and other fun electrical stuff.. ps..they call it 2-wire even though you see 3 physical wires..Ground isn't counted..ie above pic is probably sold as Romex 14/2 with ground All for now..me..licenced electrician
__________________
" Want some whiskey in your water, Sugar in your tea...What's all these crazy questions you asking me...This is the craziest party that could ever be..Don't turn on the lights cause I don't want to see..Open up the window, Let some air into this room..Think I'm almost choking from the smell of stale perfume..And that cigarette your smoking bout scare me half to death..Open up the window sucker, let me catch my breath.."I'm Governor packn2puff and I approve this message Newest!! BubbleDust Picfest |
|||||||||
|
#38
|
|||||||||||
|
|||||||||||
|
Quote:
Quote:
Ugly's is a great book to have... Also, Lowes and Home Depot have alot of other general electrical books that are good for learning the basics of home wiring.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
|||||||||||
|
#39
|
|||||||||||
|
|||||||||||
|
Quote:
In multiwire branch circuits, the continuity of a grounded conductor shall not depend on device connections such as lampholders, receptacles, and so forth, where the removal of such devices would interrupt the continuity. This has been in there since at least the 2005 code book.. Quote:
Sorry I tried to help a little..not trying to stir things up..but I do this for a living..mostly commercial & industrial..sometimes residential
__________________
" Want some whiskey in your water, Sugar in your tea...What's all these crazy questions you asking me...This is the craziest party that could ever be..Don't turn on the lights cause I don't want to see..Open up the window, Let some air into this room..Think I'm almost choking from the smell of stale perfume..And that cigarette your smoking bout scare me half to death..Open up the window sucker, let me catch my breath.."I'm Governor packn2puff and I approve this message Newest!! BubbleDust Picfest |
|||||||||||
|
#40
|
|||||||||||
|
|||||||||||
|
Quote:
Quote:
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
|||||||||||
|
|