#141 |
|
Chem D all day.....
Join Date: May 2004
Location: Kush Kanaveral
Posts: 703
![]() ![]() ![]() ![]() |
OK Ok, so 10/2 throughout no prob.You guys seem to think its going be tough to wire all that in the gang box using that ga wire?I'm going to try.I'll post it up here when I build it maybe then someone can make sure I did it correct.Thanks for all the help again fellas.
|
|
|
|
|
|
#142 |
|
Member
Join Date: Mar 2009
Posts: 752
![]() ![]() ![]() ![]() |
A quad gang box has AMPLE room. One 10/2 coming in with a total of 12 pig tails and 4 blue wirenuts .... Sure. It's going to be tight. That's why you stuff your wires to the back of the box. It won't be over cubed, I can almost guarantee that. Remeber grounds count as one and you will have no internal clamps.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
|
|
|
|
|
#143 | |
|
Chem D all day.....
Join Date: May 2004
Location: Kush Kanaveral
Posts: 703
![]() ![]() ![]() ![]() |
Quote:
|
|
|
|
|
|
|
#144 | |
|
Chem D all day.....
Join Date: May 2004
Location: Kush Kanaveral
Posts: 703
![]() ![]() ![]() ![]() |
Quote:
Again you lost me here.over cubed?grounds count as 1 what?internal clamps what is that exactly? |
|
|
|
|
|
|
#145 | |
|
Member
Join Date: Mar 2009
Posts: 752
![]() ![]() ![]() ![]() |
Ugh.... Being Overcubed is an electrician's term which means you have too many wires inside a gang box. You are only allowed to put X amount of wires in any given gang box because of heat related issues. There needs to be surrounding air around the wires so they can dissipate heat, thereby not damage the individual conductor insulation.
Look at table 314.16(A). If I'm not mistaken (I very well could be), the last "device" box you see (4 x 2 1/8 x 2 1/8) is probably a handy box. Looks just like the 4 gang one I posted earlier only it accepts ONE device. A handy box is typically what you would masonry screw to your basement wall for a light switch or receptacle box. So.... If we are going by those dimensions for just one gang, look to the right in that column and you can see what amount of wires in cubic inches it can hold safely, which is 14.5 in. If you even look further to the right, it flat out states that it can safely hold 5 #10awg conductors. We are using a 4 gang box. The only dimension that has changed is the length of the box. Therefore we can safely say that we have 58 cubic inches to work with and we can have 20 #10awg conductors in there without being illegal. Here are some rules when calculating box fill: 1.) Each device counts as 2 conductors 2.) All grounding wires just count as one conductor 3.) All internal clamps (ones that come with the box) count as one conductor Ok. You want 4 6-30R's in there. That counts for 10. 2.5 cubic inches a piece. All ground wires count as one, so add another 2.5 cubic inches. Now we have a total of 12.5 cubic inches so far. We have no internal clamps because we will be using an external NM or set screw clamp so we don't have to worry about that. Receptacles= 4x2.5 = 10 cubic inches Grounds = 1x2.5 = 2.5 cubic inches Incoming hot conductors= 2x2.5 = 5 cubic inches Total box fill = 17.5 cubic inches You've got 11 #10awg conductors there (2 incoming hot, 1 incoming ground and 8 hot pigtails). Look at table 314.16(B). Each #10 counts as 2.5 cubic inches.Pigtails and wirenuts do not count towards your box fill as per 314.16(B)(1). Quote:
Even if we counted up ALL the conductors, incoming and internal only(pigtails), that leaves us with 27.5 cubic inches just for the wire. Add another 10 cubic inches for the receptacles and that gives us a grand total of 37.5 cubic inches. We are still good.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit Last edited by madpenguin; 11-04-2009 at 07:33 PM.. Reason: Screwed up the math on box fill |
|
|
|
|
|
|
#146 | ||
|
Member
Join Date: Mar 2009
Posts: 752
![]() ![]() ![]() ![]() |
Quote:
This is really all I could find on the internet: This is what your supposed to do with your incoming grounding conductor when using a metal box: Now if you were using type MC cable, as per my example, inbetween the grounding screw that fastens to the box and where the cable enters the box, it would have a green sheath. After the grounding screw, you would strip the rest of the green sheath off and use the rest of that piece to pigtail to your 4 green sheathed gounding leads (the ones I posted earlier). Quote:
Do the same thing again with a new piece of 10/2 romex. Now you have 4 black conductors and 4 white conductors. Each piece is 6" long. Those are your pigtails. Those are what you will wirenut to your incoming feed for the metal box that will hold your receptacles. Wirenut all 4 black pigtails to the incoming hot black conductor. Each one of those 4 black pigtails will attach to one side of your 6-30R receptacles. Do the same thing to the white conductors. Only put a piece of black tape around each one so as to identify them as hot conductors. Pigtail all the whites together with a large blue wirenut and connect each of the 4 pigtails to the other side of the receptacles. This is all just basic wiring man. Go down to Lowes or home depot and buy one of those Black and Decker home wiring books. Read it. Books like that will teach you the basics. You need a basic understanding of general wiring practices before you go messing around with this stuff.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
||
|
|
|
|
|
#147 |
|
Chem D all day.....
Join Date: May 2004
Location: Kush Kanaveral
Posts: 703
![]() ![]() ![]() ![]() |
Actually that was exactly what I needed MP.Perfect.Now I can do it no prob.There was a couple minor details about how to go about it in your first explanation that I couldnt wrap my brain around but no I got it all.Thanks alot!!!nuggler
|
|
|
|
|
|
#148 | |
|
Ubiquitous
![]() ![]() Join Date: May 2007
Location: Omniverse
Posts: 5,277
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
MP, i know the NEC like the back of my hand, thats my job.
im fully licensed, business permit and working. i got a handful of guys that work for me, been doing this along time. but i'll be honest w/ you. you sound more like an EE than an "on the job" sparky IMO. i'm still gonna stick w/ what i said. he will have 1 240v single receptacle (being duplex are about as tough to get as a despod anymore) per pigtail. no way he is gonna have a 30a draw on that. only way it will happen, is if there is a dead short. it will be for a millisecond, and top out at w/e AIC the branch circuit breaker has. being most likely a residential joint, i'd say no more than 10k AIC. that is pretty much the only thing i could see happening that would justify a draw over the 5a he will have plugged into it. unless the OP does something crazy (like make a plug/box setup/ splitter) it will never be a problem imo. just like the nema r-30's, redundant imo. i'm not saying you dont know your shit, its apparent with your posts. i could sit here and quote the nec, nfpa or my law books for you all day if you want, i'm just trying to be practical.
__________________
What strain blows Frank's mind??? Quote:
R.I.P. George Carlin the funniest man to ever walk god's green earth. R.I.P. Buckeye
|
|
|
|
|
|
|
#149 |
|
Member
Join Date: Mar 2009
Posts: 752
![]() ![]() ![]() ![]() |
It's not that I don't see your point. Yes, each receptacle will probably never see more than what the ballast draws nor will the pigtails that feed them. I'm most certainly not an electrical engineer. I'm a field residential electrician. The NEC is scripture and I take it very seriously. Why you don't is a little confusing to me. If your licensed and insured but advocate your said practices on your own jobs........ Man. Your a law suit waiting to happen.
If you use a 30A OCPD, you MUST MUST MUST MUST MUST use 30A rated cable the whole way along with 30A rated receptacles. Atleast if you want to stay 100% safe you "must". Read my sig. I will not violate the NEC under any circumstance. Well, almost any circumstance. I have my lamp cords running through drywall that I then spackled up because I didn't want the extra heat in my room. Yep. That's a violation with flexible cord. I did it anyway. What I've done and what you propose are 2 completely different things and differ significantly in degree of danger posed. It's up to the OP what he wants to use as far as wire guage. I'm stating what is required as a "minimum safety standard". I'm tired of saying that phrase because people just aren't getting that that's what the NEC is all about. It's a guideline for Minimum safety standards. When you don't even meet the minimum, wow.... your asking for trouble.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
|
|
|
|
|
#150 | |
|
Member
Join Date: Mar 2009
Posts: 752
![]() ![]() ![]() ![]() |
Quote:
You got lost in the shuffle. Sorry. As long as it's a double pole and disconnects both hots when off, then sure. While killing one hot will turn off a 240v device, as well as some electricians around here saying that it doesn't matter if only one leg is dead, You will be in violation of the NEC unless both hot conductors are killed at the same time. This is like people using single pole T-stats on 240v baseboard heaters. Extremely freaking stupid and a good way to kill someone while servicing said equipment. Yea, unless the t-stat can be locked in the "off" position, you can't technically consider it as a disconnecting means but a little common sense is called for. If you have a 240v device, what ever controls said device should kill both hot conductors for personal safety reasons. Not too sure I'd trust thos SSR's anyway..... I think they are way more prone to failure than a mechanical one. That's just my opinion tho...
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
|
|
|
|
|
|
|
|