#131 | |
|
Member
Join Date: Mar 2009
Posts: 752
![]() ![]() ![]() ![]() |
Quote:
Looks pretty easy to me. 10/2 with ground on a 30A double pole breaker in your main panel. Put a black piece of tape around the white wire that attaches to the 30A breaker. Both black and white wires will attach to the 30A DP breaker in the main panel. Attach the bare ground wire to the neutral/grounding bus terminal in the main panel. If you have exposed joists in the basement, use a 3/4" auger bit to drill thru the joists. Drill right through the center of the joist with relation to top and bottom. Also, try to stay near a concrete wall. Try not to drill through the middle third span wise of a joist if that makes sense. These holes are to fish your 10/2 with ground through. Buy a piece of grey electrical conduit at Home Depot. Once you want to take the 10/2 down the side of the basement concrete wall, attach the grey electrical conduit to the wall with masonry screws and 1/2" pipe clamps to secure the electrical conduit. Just push your 10/2 down the conduit until it comes out the bottom. Looks like there is a knockout on the side of the timer. Buy a white plumbing elbow or something to mate with the electrical conduit so you can run the 10/2 into the timer so no cable is exposed. Mount the timer to the concrete wall with masonry screws as well. With me so far? Everything securely fastened.... Take your incoming black wire and attach it to terminal 1. Take your incoming white wire and attach it to terminal 3. Take the incoming bare wire and attach it to the ground screw. Put a piece of black electrical tape arond the white wire in the timer box. Buy some MC cable that has 10/2 with ground. Run it out of another knockout in the timer box. The green sheathed wire attaches to the grounding screw. The black wire attaches to terminal 2. The white wire (put a piece of black tape around it) attaches to terminal 4. Take this length of 10/2 MC (Metal Clad) cable and run it how ever far you need to get it to where you want your receptacles. Buy a quad gang box. Try to use the metal ones. Take the MC cable through one of the middle knockouts. Unless your really skilled with a hack saw, you'll want to buy some MC cable cutters. The roll of MC you bought should come with redheads (anti-short bushings). Cut enoungh of the jacket off the MC so you have atleast a foot of conductors sticking in the quad metal box. Use a metal NM connector to securely fasten the MC cable to the metal box. So once you install the redhead into your freshly cut MC cable (to protect the inside conductors from getting damaged on the rough cut edges of your MC outer sheathing, tighten down the NM connector until the MC cable is held securely in place. Now you have about 12" of green, black and white conductors in the quad metal box with about 3/8" of MC cable jacket entering the box. Get a green grounding screw. These can be had at Lowes or Home depot as well. Strip atleast 6 inches of the green insulation off until your left with bare copper conductor. Find a hole in the quad metal box that one of those green grounding screws fit into. Start threading it just a couple turns so it stays. Take your stripped green insulated conductor and wrap it around the grounding screw paying close attention that when you tighten the grounding screw down all the way, it will pull the bare conductor tight and not squeeze it out. Once the green grounding screw is really torqued down, You should have bought atleast 4 grounding leads from Home depot or lowes as well. Actually, forget about buying the grounding screws separate because we can use the ones that come with the pigtails. Whatever few inch piece of bare copper is left from when you tightened down the grounding screw, take a pair of linemans pliers and mechanically twist all the grounds together. Then wirenut 4 of the above grounding pigtails to the bare copper conductor that is attached to the back of your box. You'll need the big blue wirenuts for this. When your using linemans pliers to mechanically twist wire together, use very little force at first. Kind of let the wire slip through the plier heads. With each turn of the wrist, put more pressure on the bare copper wire that your trying to twist. You will eventually get all of the ends of wires to line up with each other and it will look like(and be) a really nice electrical connection. If you just really clamp down on all the wires at once and then twist really hard, wires will slip out and it'll look like shit and you'll have to do it over again. Sounds silly but there actually is a correct way to twist wires together. You'll figure it out. Cut about a foot piece off of any left over 10/2 with ground romex and get the black and white conductors out of it. Put black pieces of tape around 4 white wires and then you should also have 4 black wires. Wire nut all the blacks together (including your incoming black lead from the timer box). Do the same with the white wires but make sure each white wire has a piece of black electrical tape around it. Now you have 4 black wires, 4 white wires and 4 green wires inside your quad gang metal box. Need I continue? These are 240v receptacles. Put a black on one side and a white on the other and then a green on the grounding screw of the receptacle. Do that for all 4 receptacles, then find a metal box cover that will work with your receptacles. If there are any plastic round or square thing-a-ma-bobs holding the mounting screw for the receptacle in place, remove those. You want metal on metal contack with the yoke(strap) of the receptacle to the metal of the box.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
|
|
|
|
|
|
#132 |
|
Member
Join Date: Mar 2009
Posts: 752
![]() ![]() ![]() ![]() |
BTW, try to get most of this stuff from a local electric supply house unless ofcourse it's cheaper at Lowes or Home Depot.
Have I ever seen 10/2 w/ ground MC cable at Lowes? Dunno. The only reason I suggested MC cable is that I have a feeling your just going to have your wire laying all over the place such as on the ground. Remember romex can not be exposed to physical damage. Make sure you fish that stuff through the cieling joists of your basement and then sleeve it with EMT (Electric Metalic Tubing) or the gray Electrical tubing you see at Lowes. Romex is VERY subject to damage. We had an arguement on whether or not to use NM connectors a day or so ago with NM and the answer is an EMPHATIC YES! That sheathing will get damaged if you just breathe on it wrong.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
|
|
|
|
|
#133 |
|
Senior Member
Join Date: Dec 2007
Location: Planet Stupid
Posts: 1,612
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Madpenguin - I'm not going to argue code with you, since I'd lose, but... As far as using #12 or #14 for the final few inches (the pig-tails) that go to the receptacles, there's nothing wrong with that. You're not trying to pull 30 amps per receptacle for crying out loud, only 5. Think about it this way - the receptacle box he is making is basically an appliance and the internal wiring of the appliance doesn't have to follow the same rules as the circuitry bringing the power to the appliance. We could pick nits all day long about how to define the four gang box and its contents, but I think you get my point. 10 ga. wire just isn't necessary for the pigtails and would make the wiring a lot more difficult.
Trying to do all that wiring in a little bitty box with all #10 wire would be a major PITA that simply isn't necessary. Danknuggler - you are going to be running a piece of cable from your timer to your receptacle box. Inside that cable are 3 #10 wires - Black, white and bare (or green). Each of those wires is called a leg. The black and white legs are hot, the bare/green is a ground. To each of those three #10 wires you need to attach (wire nut) four more wires. Those wires are called pig-tails. Each pig-tail goes to a receptacle. You can make those pig-tails out of #12 or #14 wire, either one is sufficient to carry the load you envision. Trying to make all of those pig-tails out of #10 wire and then trying to stuff everything into the four gang box would be very difficult, and foolish, especially since there is no good reason to use such big wire for your terminal connections. PC |
|
|
|
|
|
#134 | |
|
Member
Join Date: Feb 2007
Location: Quebec/Canada
Posts: 946
![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Quote:
__________________
Sorry for my writing skill english is not my first language. ![]() peace to all |
|
|
|
|
|
|
#135 | ||
|
Senior Member
Join Date: Dec 2007
Location: Planet Stupid
Posts: 1,612
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Quote:
Quote:
PC |
||
|
|
|
|
|
#136 | |
|
Ubiquitous
![]() ![]() Join Date: May 2007
Location: Omniverse
Posts: 5,277
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
i'm still gonna say the 14/12 jumpers are ok.
only because, as stated earlier, each 240v receptacle will not draw over 4.5amps. how many times has any electrician fed a machine with a large line, only to have the guts of that machine run its factory wiring w/ smaller size wires than the feed line? most of the time, the controls and inner working of a machine have ocp on the factory wiring, but not always. this would be no different. also, using nothing but 30-r's is redundant. not to mention ganging them up in a box is not gonna happen. i feel like my advice was sound and correct. i've only been a licensed electrician for a handful of years, but i been doing this work since last century!
__________________
What strain blows Frank's mind??? Quote:
R.I.P. George Carlin the funniest man to ever walk god's green earth. R.I.P. Buckeye
|
|
|
|
|
|
|
#137 | |
|
Senior Member
Join Date: Dec 2007
Location: Planet Stupid
Posts: 1,612
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Quote:
PC |
|
|
|
|
|
|
#138 | ||
|
Member
Join Date: Mar 2009
Posts: 752
![]() ![]() ![]() ![]() |
Quote:
Quote:
PC and Cocktail frank, you are overlooking something extremely important that should have been learned by any first year apprentice. They are called Articles 210.20(B) and 240.4. If you guys do any electrical work on a regular basis, I strongly suggest you familiarize yourself with the NEC. Besides the below articles, common sense would tell ANYONE that you need to use the same gauge throughout the entire circuit. 210.20 Overcurrent Protection. (B) Conductor Protection. Conductors shall be protected in accordance 240.4. Flexible cords and fixture wires shall be protected in accordance with 240.5 240.4 Protection of Conductors. Conductors, other than flexible cords, flexible cables, and fixture wires, shall be protected against overcurrent in accordance with their ampacities specified in 310.15, unless otherwise permitted or required in 240.4(A) through (G). 240.4(D)(3) 14 AWG Copper. 15 Amperes. 240.4(D)(5) 12 AWG Copper. 20 Amperes So....... Again. Tell me why it is OK to use #12 or #14 pigtails coming off the #10 homerun to attach to your receptacles? Common sense will tell you you'll have an instant fire if that receptacle see's more than 15A if it's using a 30A 0CPD. I'm sorry but this is childs stuff that even the original poster knew and he's not even an electrician to my knowledge. What's your guy's excuse? I'm still gonna say you guys are DEAD wrong and anyone who listens to you runs the risk of burning their house down.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
||
|
|
|
|
|
#139 | |
|
Member
Join Date: Mar 2009
Posts: 752
![]() ![]() ![]() ![]() |
Quote:
Not insulting anyone here, but that it a time saver technique and and the sign of a hack electrician, not to mention you'll burn someone's house down.
__________________
Licensed Journeyman Electrician All Electrical advice given is based on the 2008 NEC and in no way should be listened to in the first place. When in doubt, hire an Electrician. ![]() DIY Light Controller Voltage Drop Calculations Basic wire sizes and ampacity Complete guide to wire size/type and ampacity plus How to wire a sub panel Installing a subpanel in a detached structure plus burial depth requirements Running wire and installing branch circuits Electrical Theory "Old Working" branch circuits GFCI and AFCI requirements NEMA receptacle and plug types Everything you wanted to know about Flexible cords Receptacle spacing 240v and Multi Wire Branch Circuit |
|
|
|
|
|
|
#140 |
|
Was blind but now IC Puckbunny in Training
Join Date: Dec 2007
Posts: 11,517
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]() |
Here you go Sleepy. Stickified just for you.
![]() Now gimme some magic cowbell!
__________________
. . FreezerBoy's Destroyer Diary-Completed...... FreezerBoy's Thunk Diary-Completed...... Beginners Links |
|
|
|
|
|
|
|