No.If I'm running 6 1kW lights at 4.75amps each, that 28.5amps total. Will this contactor handle that?
Did you build that? What did you use for a box and cover?10 ballast loadcenter.
TACTICIAN. DO THINK IT WOULD BE POSSIBLE FOR YOU TO START A THREAD ON HOW TO PHISICALY, BUILD A 10 LOAD CENTER STEP BY STEP INCORPORATING A PLC. OR JUST A DEATIL INDEPTH DESCRITION OF ALL THE PARTS THAT GO ALONG WITH A PLC....
I was thinking about this and wanted to make sure this is correct. If the trigger voltage is 120 and the voltage that the relay is switching on and off is 240, is this the correct relay? Also, it shows that this is a 25amp contactor. If I'm running 6 1kW lights at 4.75amps each, that 28.5amps total. Will this contactor handle that? I noticed that you said "a couple" so I couldn't achieve the desired result with only 1 relay?