Tutorial Ventilation 101

G

guest 77721

You would only stack fans in series to overcome a pressure problem. Because of the high back pressure the fans don't produce the maximum flow but will add their pressures together. If they were unrestricted the flow would be around the weakest fan's max CFM.
 

rasputin

The Mad Monk
Veteran
Redgreenry, awesome thread.

Quick question jus to be sure... flowering room is 5x5x6... I need approx. 125 cfm fan (I'm rounding up a bit for a little CYA)? I need to keep it well ventilated enough for odor to be gone and temp's to stay balanced. I was thinking of a 6" ducting fan attached to a DIY carbon filter made 12-18" in dia.

Yer thoughts?
 
G

guest 77721

Thanks Rasputin,

you're asking to do two different things at the same time.

To take the heat out of the room, you need roughly 3CFM per watt. If you use vented hoods or cooltubes and pass outside air through the tubes and exhaust it outside, you will need 0.3 CFM per watt.

A 5x5x6 room is 150 cubic feet. At an air exchange rate of once every 5 minutes you would need a scrubber that would pass 150cuft/5min = 30 cubic feet per minute

*****************************************************************
Let's design this room using some rules of thumb. 50 w/sqft is the normal size for HPS lighting. Your 5x5 room has 25sqft which would take 1250 watts or two 600w HPS.

Each 600w light would need 0.3 CFM for 180 CFM. If you series the airflow, the exhaust air would be twice as hot but it's going outside, not on the plants. Get a 180 CFM axial fan and a small scrubber rated to 30 CFM.

If you want to pass all the air through the scrubber you would need to double the size of the fan and it would need to be a centrifical blower not an axial fan at 360 CFM and the scrubber would need to be about 200 CFM.
 

BlueHalo

Member
Hey guys! I just got this link and have a vent issue that I really need some feedback on, if you have time, which would be greatly appreciated.

Ok, So I have previously been using a 55 gallon rubbermaid to grow in with 25,600 lumens of CFL's but have now built an oak cab that is 7 feet tall x 3 feet wide X 19 inches deep and have it partioned in half horizontally so that I have a mother cab in the bottom and a flower cab up top. The mother cab is using CFL's while the flower cab will be, as of tomorrow, using a 400 Watt HPS Cooltube.

I am using a 5" S&P Mixedvent inline fan-TD series 125 with 192 CFM for my exhaust which is hooked up to my attic. On the bottom of mother cab I have 12 X 1.25" passive intakes and then from the mother cab I have 10 X 1.25" intakes drilled through the shelf that seperates the two rooms. At first I only had 12 X 1.25" passive intakes + (2 X 1.25") passive intakes drilled into the shelf partition and the doors sucked shut on me and the motor strained a bit. From what I understand this is due to the negative pressure inside the cab. Then today I drilled 8 more 1.25" holes into the shelf (a total now of 10 X 1.25") partition leading from the mother room and into the flower room, but now the door no longer sucks shut from the negative pressure inside of the cab. Should I plug some of those holes up that I drilled today in order to get my pressure back? As I said I have a 400 watt HPS coming tomorrow and really need to get these vent issues straightened out ASAP. Any help that you might be able to provide would be greatly appreciated. PUFF PUFF!!

Currently growing Tundra (Autoflower), WhiteBerry, Spoetnik, and Purple Lady

I added 6 more intakes to the bottom after the photo.
 

BlueHalo

Member
Hey redgreenery I was wondering if I could increase my negative pressure inside the cab by putting the S&P on high setting? Right now I have it on low but with no speed controller. I haven't bought a speed controller because my TD 125 is a 2 speed motor and am not sure if you can actually use a speed controller on these, and if so then what kind? PUFF PUFF!!
 

rasputin

The Mad Monk
Veteran
Thanks Rasputin,

you're asking to do two different things at the same time.

To take the heat out of the room, you need roughly 3CFM per watt. If you use vented hoods or cooltubes and pass outside air through the tubes and exhaust it outside, you will need 0.3 CFM per watt.

A 5x5x6 room is 150 cubic feet. At an air exchange rate of once every 5 minutes you would need a scrubber that would pass 150cuft/5min = 30 cubic feet per minute

*****************************************************************
Let's design this room using some rules of thumb. 50 w/sqft is the normal size for HPS lighting. Your 5x5 room has 25sqft which would take 1250 watts or two 600w HPS.

Each 600w light would need 0.3 CFM for 180 CFM. If you series the airflow, the exhaust air would be twice as hot but it's going outside, not on the plants. Get a 180 CFM axial fan and a small scrubber rated to 30 CFM.

If you want to pass all the air through the scrubber you would need to double the size of the fan and it would need to be a centrifical blower not an axial fan at 360 CFM and the scrubber would need to be about 200 CFM.

Interesting, thank you Red. That is a lot more fan and scrubber than I anticipated. Luckily, I got a bead on some home depot duct fans so I don't need the expensive vortex or whatever else.

I trust yer take on the matter, you seem very well versed and nuanced on the subject. And odor is the main concern, not temps. I lazily tossed in keeping the temp's balanced and you rightly interpreted that as a need to bring them down. I don't anticipate major temp adjustments via the fan but one never knows. I intend on having 1-2 fans in the room moving air around besides the exhaust fan but the ambient temp & RH could be a problem come the summer. Blowing hot air only helps so much. :D

I picked up an Inductor 6" inline duct fan that is 250 CM. I could use your first example and that should do the trick even with a carbon filter attached? Ideally I'd have the fan facing the floor in the cieling w/the filter in front of it pulling air through & out the room. Cycle the room every few minutes and with, what say you, a 8" passive intake bringing in fresh air.

This is the step up from what I got. 500 CFM. That ought to do the trick either way I choose w/a carbon filter, no? Any thought on how wide a diameter to go on the filter w/this fan? Thanks Red.

http://www.homedepot.com/webapp/wcs/stores/servlet/ProductDisplay?jspStoreDir=hdus&catalogId=10053&productId=100396544&navFlow=3&keyword=8%2522%2Bduct%2Bfan&langId=-1&searchRedirect=8%22+duct+fan&storeId=10051&endecaDataBean=com.homedepot.sa.el.wc.catalog.beans.EndecaDataBean%403d87d72a&ddkey=Search
 

hoosierdaddy

Active member
ICMag Donor
Veteran
rasputin,
You can have a fan that pushes 250cfm, but pulls very little pressure. Another fan can also be rated at 250cfm and pull loads of pressure.
The duct boosters are just that, boosters. They cannot pull very much pressure at all. No comparison between the 250cfm duct fan and a Vortex or S&P of the same cfm rating.
I have used the duct fan attached to a carbon scrubber for my cab. Thing is, the fan doesn't have much power and it takes two of them stacked together at the end of the scrubber to pull enough to keep my cab cool. The cfm is virtually the same with one or two fans, but the pressure is increased by nearly double. (still not as powerful as one quality inline fan)
I now use one of those duct boosters to keep my 400w + 150w lights cool in a tube. And it is quite enough to do that job. Two won't help much in that situation because there is very little pressure to deal with, and two wouldn't help matters in that situation.
(hope it makes sense why...red has explained it technically)

IMO, leave the boosters to boosting and doing what they are capable of doing. Get a decent inline fan to use with the scrubber.
 

rasputin

The Mad Monk
Veteran
rasputin,
You can have a fan that pushes 250cfm, but pulls very little pressure. Another fan can also be rated at 250cfm and pull loads of pressure.
The duct boosters are just that, boosters. They cannot pull very much pressure at all. No comparison between the 250cfm duct fan and a Vortex or S&P of the same cfm rating.
I have used the duct fan attached to a carbon scrubber for my cab. Thing is, the fan doesn't have much power and it takes two of them stacked together at the end of the scrubber to pull enough to keep my cab cool. The cfm is virtually the same with one or two fans, but the pressure is increased by nearly double. (still not as powerful as one quality inline fan)
I now use one of those duct boosters to keep my 400w + 150w lights cool in a tube. And it is quite enough to do that job. Two won't help much in that situation because there is very little pressure to deal with, and two wouldn't help matters in that situation.
(hope it makes sense why...red has explained it technically)

IMO, leave the boosters to boosting and doing what they are capable of doing. Get a decent inline fan to use with the scrubber.

Hoosier, thanks for the info. I suspected I'd get a similar reply from Red, altho' I was hoping not. Looks like I can use the 6" for blowing air around at least or just return it. Maybe hook it up in the veg room for some air movement. Time to search for some reasonably priced inline vans.

Ah! I just caught your mention of using the duct boost to cool your lights. I could use this 6" fan to connect to the air cooled hood and let it fan the bulb. Then I can get a better fan to hang in the room w/a filter as a scrubber or exhaust.

EDIT

Alright, I had to come back here. Got into a little discussion with an acquaintance about CFM's and fans and air circulation and he's adamant, lo and behold he has an architecture degree! oh my, so in his estimation I was "fucking stupid" for listening to people I don't know on-line tell me that the 250 CFM duct fan isn't enough to vent a room. How it came up in discussion was innocent so no worries that I'm discussing my op with anyone who doesn't need to know. :)

If that isn't funny enough, when I tried telling him how a duct 250 cfm is like a Vortex is 250 cfm but pulls different amounts of pressure he couldn't understand it. Now, truth be told, I'm a little torn on it but I understand it. A bathroom fan versus a computer fan or even an oscillating bedroom fan aren't exactly the same kind of fan even if their CFM rating is similar. He doesn't get that. I don't know an easier way to explain it to him and frankly, I'm tired of having this discussion with him. He doesn't know I'm growing but he's a friend of a good friend of mine so he's often my friends house. And lately we've been casually discussing building and whatnot, it's a fairly typical topic over there so it doesn't raise any eyebrows, and so my friend and I discuss all this under the premise of building a music room in the basement.

He's chimed in the last few weeks and it's grown to a point where I just want to say, hey look you've never had to do any of this before and I'm pretty sure your degree didn't teach you shit about removing the dank odor of marijuana plants out of your grow room. But for good reasons I'm not going there. :D
 
G

guest 77721

Hey guys! I just got this link and have a vent issue that I really need some feedback on, if you have time, which would be greatly appreciated.

Ok, So I have previously been using a 55 gallon rubbermaid to grow in with 25,600 lumens of CFL's but have now built an oak cab that is 7 feet tall x 3 feet wide X 19 inches deep and have it partioned in half horizontally so that I have a mother cab in the bottom and a flower cab up top. The mother cab is using CFL's while the flower cab will be, as of tomorrow, using a 400 Watt HPS Cooltube.

I am using a 5" S&P Mixedvent inline fan-TD series 125 with 192 CFM for my exhaust which is hooked up to my attic. On the bottom of mother cab I have 12 X 1.25" passive intakes and then from the mother cab I have 10 X 1.25" intakes drilled through the shelf that seperates the two rooms. At first I only had 12 X 1.25" passive intakes + (2 X 1.25") passive intakes drilled into the shelf partition and the doors sucked shut on me and the motor strained a bit. From what I understand this is due to the negative pressure inside the cab. Then today I drilled 8 more 1.25" holes into the shelf (a total now of 10 X 1.25") partition leading from the mother room and into the flower room, but now the door no longer sucks shut from the negative pressure inside of the cab. Should I plug some of those holes up that I drilled today in order to get my pressure back? As I said I have a 400 watt HPS coming tomorrow and really need to get these vent issues straightened out ASAP. Any help that you might be able to provide would be greatly appreciated. PUFF PUFF!!

Currently growing Tundra (Autoflower), WhiteBerry, Spoetnik, and Purple Lady

I added 6 more intakes to the bottom after the photo.

Hey BlueHalo, your plants look lovely. I think they will like their new home once we get it fixed up. Who say's you can't grow in a Rubbermaid - eh!

I started looking at the calculations to open up the airflow and I realized that your fan is quite a bit oversized. A bare 400W HPS needs about 120 CFM with a 10*F temperature rise. With a cooltube the airflow can be cut by about 1/3 so 40 CFM is all that's needed.

I was going to tell you to cut a 6.5" square hole in both the shelf and the floor but knowing you have too much fan I wouldn't change anything until you get the lights in.

I'm thinking about the health of the plants. They won't grow well in a wind tunnel so it would be best to install your lights and see how the temps look and drill holes as needed. 40 CFM would give you 1 Air Change Per Minute.

I would install a 8" darkroom vent in the shelf to lightproof both sections and drill holes in the mother floor as needed.
 
G

guest 77721

Hey redgreenery I was wondering if I could increase my negative pressure inside the cab by putting the S&P on high setting? Right now I have it on low but with no speed controller. I haven't bought a speed controller because my TD 125 is a 2 speed motor and am not sure if you can actually use a speed controller on these, and if so then what kind? PUFF PUFF!!

http://www.solerpalaucanada.com/Soler Palau Canada TD Brochure Oct 2006 web.pdf

The S&P says your two speed TD125 motor is a shaded pole induction motor suitable for Voltage Speed Control.

If you want to wire it to use the high speed, low speed modes, you will need two speeds. I have a feeling you will be running on low speed.

When you do get a speed controller, you can wire it to the high speed or low speed windings. Or put a switch on the high speed and wire the controller to the low speed. Lot's of options.
 

BlueHalo

Member
Thanks redgreenery for the help. When I did my posting I said that the cab was 7' tall but I was toasted to a crisp and got it wrong, sorry. The cab is actually 5'8" tall. I don't know id that makes any difference. As far as the exhaust goes I am exhausting the whole cab and not just the bulb. Some will exhaust the bulb seperately and then exhaust the cab
with another fan but I thought that that would add some unneeded costs to the project.

If I put too many intakes in then wouldn't I just loose negative pressure inside of the cab and then heat issues? Having the doors suck shut is a good thing, right? Once I get everything hooked up and see where the temps are then I'll post again. PUFF PUFF!!
 
G

guest 77721

Hey Rasputin and Hoosier

there's lot's of fan designs out there and they all have an application that they fit. Your Architect buddy sounds typical.

Axial fans like a computer fan, or an oscillating fan move a lot of air.

Centrifical Blowers are made for pushing against a high static pressure restriction and are suitable for long duct runs and filter applications.

There's the mixed type like the S&P's that are more like a jet Airplane turbo jet that mixes axial and centrifical technologies.

Hope this chart helps.



The biggest question is do you want to move a lot of air or push it hard through a restriction. I think it's better to move a lot of air through your lights and a small amount through a scrubber using separate fans.
 

hoosierdaddy

Active member
ICMag Donor
Veteran
rasputin,
Surely your friend isn't so obtuse that he can't visulize the difference between a duct booster and a quality fan, rated at the same CFM?

Look at it this way...a 250cfm duct booster may push around 250cfm when it is running with no duct hooked front or back, just sitting there running. But the second you place a duct run to one end or the other, static pressure of X amount is placed on the air passage, and the fan must now work harder to try and keep the same cfm as before.
That amount of static pressure is determined by how long the run is and how much friction it creates, among other interesting but moot occurrences.
A run that creates .5 inches of static pressure will cause a S&P 6" to run about 206cfm. That same run would choke a duct booster down to about 20cfm or less. Virtually useless.

They don't run the cfm that they are rated at unless they are naked with no duct. OR, they have a powerful motor to make up for an increase of pressure..like a quality fan does. If it were as simple as your pal thinks..we could all just use 25$ boosters.
 

rasputin

The Mad Monk
Veteran
Just venting... :)

Just venting... :)

Each 600w light would need 0.3 CFM for 180 CFM. If you series the airflow, the exhaust air would be twice as hot but it's going outside, not on the plants. Get a 180 CFM axial fan and a small scrubber rated to 30 CFM.

If you want to pass all the air through the scrubber you would need to double the size of the fan and it would need to be a centrifical blower not an axial fan at 360 CFM and the scrubber would need to be about 200 CFM.
To cool the light I can use the duct fan I bought and say, a 6" DIY filter? On top of that, get the 360 centrifugal and the bigger filter? Damn, this is getting expensive for just a 5x5 flowering room.

Thanks for your continued help, Red, it's greatly appreciated.
 
Last edited:

hoosierdaddy

Active member
ICMag Donor
Veteran
If you are already a weed smoker, figure up how much you spend on it.
It helps the money issue when you place it all into perspective.
 

rasputin

The Mad Monk
Veteran
If you are already a weed smoker, figure up how much you spend on it.
It helps the money issue when you place it all into perspective.

Yeah, that is how I've been looking at it this whole time.

360 CFM will give me 25% additional circulation in the room, should be enough to circulate the entire room which is roughly 8x8x6.

Light --- > Fan --- > --- Filter/Exhaust

Thanks fer the help, fellas.
 
Last edited:

MoleMcHenry

Member
Ventilation question about a potential setup

Ventilation question about a potential setup

Hi Red and other ventilation experts,

I've been thinking about changing my setup and was wondering if you think its feasible.

In the grow space, which is a ground floor bedroom with lots of fresh air flow, I am currently running a 3x3 with 2 x 400s and a 145 cfm 4" fan/fliter just fine, and the lights are not even air cooled. I want to raise my yields, so have a been thinking of a new setup. Here's a diagram I made to show you what I'm thinking. I got the idea from one of Texas Kid's posts.



The new setup would be in a 40"x40"x78" silver Hydrohut located in in the same bedroom. There would be separate venting systems for the lights and the interior of the tent.

I would have 2 air-cooled digital 600's vented with room air that is sucked over the lights before it is vented out of the opposite side of the tent. The fan for the lights would be a 294 cfm S&P 6 inch fan. I would probably put this fan outside the tent. All the ducting would be R6 or R8 insulated flexible ducting.

I would vent the interior of the tent with an identical 294 cfm S&P fan that sucks tent air through a 6 inch Carbonaire filter rated 200-500 cfm before pushing it out of the top of the tent.

In addition to the insulated ducting, I would also use those insulated reflector covers called Sun Shields which are supposed to significantly improve room temperatures.

I like the idea of using 2 600's because it would be great for the scrogs I have to do to remain within legal limits in my state.

So my question is: what do you think of this potential setup? What do you think I should do differently? Thanks in advance for your help.

Mole
 

BlueHalo

Member
Hey Ya'll ! I just got my cab all put together. I got my 400 watt HPS and Metal Halide Conversion bulbs yesterday along with the Batwing reflector, but I scratched that one after I saw how small it was. Instead I built my own reflector out of Hvac pipe which is the full width and depth of the cab (3.6' X 19"). I lined it with some Reflectix that I had laying around from my Rubebrmaid Grow. I built the Cool tube out of a Bake A Round from Ebay and initially had it hooked up to the exhaust with that crappy slinky type of dryer hose but was loosing pressure and so instead I hooked it up using 2 X Hvac 90 degree elbows. I just put in the 400 Watt Metal Halide bulb and DAMN this is BIG and definately BRIGHT!! I had to wear sunglasses in there. The bulb just barely fit inside of the Cooltube. I hope that the tube can withstand the heat. Anyways, I closed the doors to see if I had any negative pressure in the cab and guess what ? I don't. The doors no longer suck shut.
I got some heat coming off of the Cooltube but for only like a foot. I am sure that once I get some negative pressure back in the cab that heat will subside somewhat. I really need some advice on how to get the negative pressure back into the cab? Any one, please. As some may remember from my last posting I have 12 X 1.5" passive intakes in the bottom of the mother cab. From there I have 2 X 1.5" intakes through the Mother cab shelf and up and into the flower cab. Today though I put 3 more intakes into the flower cab to see if that would help but there was no negative pressure to be had. And so I closed them back up with reflective tape. Any sugesstions would be greatly appreciated. PUFF PUFF!!!

Sorry for the crappy pics.